what is the best way to put 230v single phase circuits onto a db with a 3phase 3 wire system with no neutral connection........
 
is this Db a submain? Then rewire it with a new (swa?) with a neutral. I have converted 3 phase boards to single phase using a conversion kit, but there was a neutral there. No neutral = no chance. Unusual set up for a db though to be honest.
 
exactly thankyou...... i am havin a debait with a freind and you answered my question for me........
cheers lads...
was debaiting that in old typ of supply that becasuse the 3 phases are delta are 120 deggrees out of phase with each other , thaat you could put a single phase circuit on the said system, with out a neutral?????
 
Last edited by a moderator:
old type of supply?

3 phase is still 120 degrees apart!

I have just posted on your other thread having just read it.

I suggest you calm down, take a deep breath and think for a moment, then try to articulate, starting from the beginning, what you have in front of you, and what you want to achieve at the end of it.

Breathe, now, breathe....
 

Reply to 400 v & 230v circuits in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

  • Question
I may have been mistaken regarding TT I will look into that, thank you for the valued reply, but in general I stick to my post, a good topic for...
2
Replies
24
Views
3K
Found the cause of the tripping…. Just jointed them through… all clear now. Removed the smoke detectors completely. They were due to be...
Replies
6
Views
855

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top