W
woko
When using these inverters I've been told you have to ground the array with an earth spike ( not using the MET) and install a 100 ma RCD.
According to the DTI if the house earthing System is TNC-S then yes apparently you have to earth the frame to a rod.
According to the manufacturers instructions apparently you need to fit a 100mA RCD, but if your burying cables less than 50mm and they do not have any protection as per 522.6.6 then that 100mA must be a 30mA
I have such a beasty and, not being an electrician, was told the earth was required because it is Transformerless and DC faults can therefore pass to the AC (grid) side. Evo also installed a separate RCD
Reply to 400TL Sunny Boy in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net
You can use timers to turn ON/OFF circuits during the day to maximize your self-use of solar power. Turn ON low draw circuits such as a 1Kw pool...
Do you have a test meter of any kind? if so, disconnect all four wires that go into the motor and check for a low resistance between them. You...