A
Ago4Ago
EICR on a Factory. I came across a consumer unit in an outdoor shed feeding a double socket (with a 4 way trailing lead with neon, plugged in) and 2 lights. Trying to locate where this consumer unit was fed from I plugged in a socket tester (one with the three indicator lights & a shrill beep). This indicated that there was a problem with the earth. I then plugged in my Earth Fault Loop tester to see what the Zs was; No reading. I then plugged the socket tester back in & only the right hand indicator light lit up this time, referencing a reversed line & earth as apposed to all 3 with a flickering left hand one as before; I then knocked the isolator off at the consumer unit & removed the cover, to find 400V between Line & Neutral. 230v between L&E and N&E. My question is: Could, trying to take a Zs reading from the socket have disturbed something earlier in the system to create 400v across L&N ??:confused: As I am only employed to inspect & test on the condition of the installation. I isolated the circuit & did not investigate further at this point.
or has some numpty wired it across 2 phases?
Sure looks like it, and I think the "comprehensive" plug in tester is now toast.
And this is a worrying Question from someone who tests;
Surely it would have blown any thing that had been plugged into the trailing lead or at least the neon? It is just puzzling me because as much as I would have liked to; I just hadn't the time and wasn't being paid at this point to investigate further.
The plug in tester is primarily used as an audible devise to listen when the circuit is disconnected but also gives an instant indication as to anything adrift. And no it isn't Toast
This particular job is the worst I have ever seen in 30 years. The outside shed Scenario is just part of a catalogue of examples of very dangerous practice. I was warned not to look too deep, by the owner. However I have a reputation to protect as he has an obligation to protect his employees. Therefore it is being tested and inspected to BS7671 full stop.
As the impedance of the phase-to-earth loop is measured by connecting a resistor (typically 10 Ohms) from the phase to the protective conductor. A fault current, usually something over 20 A, circulates in the fault loop, and the impedance of the loop is calculated within the instrument. I was just wondering if anyone had had any experience of this creating a problem that might explain the reason for the appearance of 400v between L&N. Not sure why the criticism on posing the question?
There's no way using a tester in the manner it was designed can alter the characteristics of a circuit such that 400v appears where you'd normally get 230v.
And if you are finding more examples of dangerous practices and the owner has warned you not tolook too hard, it begs the question should the installation still be in use by anyone, other that a tester, untill found to be completely safe?
I agree totally, the factory is closed at the moment due to Christmas and there is only myself & a colleague in the premises. I don’t think I have any powers to enforce the closure of the factory until in a safe condition. I can only submit a report to the “responsible person” emphasising the fact.
I dont know what limitations you have agreed and you say you have isolated the CU in the shed.
I would be looking at what feeds the CU and you will most likely find as Tel has said it has been wired wrong and is fed by 2 phases.
Its then down to you what codes you issue and if a code 1 I would be issueing a dangerous notice to the person ordering the EICR.
Agreed, problem is; disboard feeding CU in shed has been boxed in making it impossible to take the front off. So for now I have switched the 3 phase mcb feeding it off. The thing is. The circuit to the shed and the circuits from the CU in the shed look like they have been there some time, so I cannot see that there has always been 400v between L&N. I have logged it as a C1 also requiring further investigation.
It is just puzzling me as to how it has come about. Hence; throwing it in here in case anyone has any similar experiences.
well, if the DB has been made inaccessible by boxing in, ytou need one of these builders' precision tools. make sure it's in calibration.
If you are testing throughout the factory it could be the case that a Neutral has been left disconnected and a floating neutral created between phases which can rise the voltage in excess of 400v on a single phase load, you can easily check the origin of the circuit to see if it is truely been tagged as a bodgit 2ph or is in fact connected as 1ph.... if the latter then a floating neutral is a highly likely situe and fingers crossed you aint blown any connected single phase loads throughout the factory.
A faulty 4pole switch contact on the neutral can cause this but im sure you have followed protocol and had all outgoing circuits isolated before switching back on and voltage check before re-energising.
Thanks Darkwood. I would like to discus further with you but your private message seems to be full.
Lost neutral.
Seen it before, 380v at a 13a skt.
What is suposed to be the neutral is returning through the other phases, like an unearthed star point.
Boydy
forgot to mention the calibration procedure for sledgehammers.
1. hit a plumber over the head with the hammer under test.
2. accurately measure, with a stopwatch, how long it takes from the impact with the hammer to the impact with the ground.
3. anything under 5 seconds, the hammer passed calibration.
4. if the installation is TT, however, you need to hit him twice. TW*T, TW*T.
Bingo! Dismantled half a staircase to gain access to Dis-Board feeding Consumer unit in question & sure enough a burnt out neutral. Not originally tightened enough by the looks of it.
Glad you found it .... bill as extra emergency repair keep any evidence or take pictures, be cautious of the damage the heat has caused if like where it was clamped if major discoloration has occured it best to replace the busbar or terminal bar when you get the chance as the heat will have altered the metal and it can become a weak point and re-occur.
I got 400v at a 16a single phase socket one time doing a periodic. Couldn't believe my eyes, switched meter on/off a few times and the RCD, still got 400v. Socket was wired on the yellow phase, turned out flood light on the red phase had melted phase to cpc. Incoming earth had been disconnected from the HV transformer hence 400v live to earth lol. The mind boggles sometimes.
400V between L&N
Thread Tags
Tags Tags
between
Ago4Ago,
C&H,