Ago4Ago

EICR on a Factory. I came across a consumer unit in an outdoor shed feeding a double socket (with a 4 way trailing lead with neon, plugged in) and 2 lights. Trying to locate where this consumer unit was fed from I plugged in a socket tester (one with the three indicator lights & a shrill beep). This indicated that there was a problem with the earth. I then plugged in my Earth Fault Loop tester to see what the Zs was; No reading. I then plugged the socket tester back in & only the right hand indicator light lit up this time, referencing a reversed line & earth as apposed to all 3 with a flickering left hand one as before; I then knocked the isolator off at the consumer unit & removed the cover, to find 400V between Line & Neutral. 230v between L&E and N&E. My question is: Could, trying to take a Zs reading from the socket have disturbed something earlier in the system to create 400v across L&N ??:confused: As I am only employed to inspect & test on the condition of the installation. I isolated the circuit & did not investigate further at this point.
 
or has some numpty wired it across 2 phases?

Sure looks like it, and I think the "comprehensive" plug in tester is now toast.

And this is a worrying Question from someone who tests;

My question is: Could, trying to take a Zs reading from the socket have disturbed something earlier in the system to create 400v across L&N ??
[ElectriciansForums.net] 400V between L&N
As I am only employed to inspect & test on the condition of the installation. I isolated the circuit & did not investigate further at this point.
 
Surely it would have blown any thing that had been plugged into the trailing lead or at least the neon? It is just puzzling me because as much as I would have liked to; I just hadn't the time and wasn't being paid at this point to investigate further.
 
The plug in tester is primarily used as an audible devise to listen when the circuit is disconnected but also gives an instant indication as to anything adrift. And no it isn't Toast
 
This particular job is the worst I have ever seen in 30 years. The outside shed Scenario is just part of a catalogue of examples of very dangerous practice. I was warned not to look too deep, by the owner. However I have a reputation to protect as he has an obligation to protect his employees. Therefore it is being tested and inspected to BS7671 full stop.
 
Sure looks like it, and I think the "comprehensive" plug in tester is now toast.

And this is a worrying Question from someone who tests;
As the impedance of the phase-to-earth loop is measured by connecting a resistor (typically 10 Ohms) from the phase to the protective conductor. A fault current, usually something over 20 A, circulates in the fault loop, and the impedance of the loop is calculated within the instrument. I was just wondering if anyone had had any experience of this creating a problem that might explain the reason for the appearance of 400v between L&N. Not sure why the criticism on posing the question?
 
As the impedance of the phase-to-earth loop is measured by connecting a resistor (typically 10 Ohms) from the phase to the protective conductor. A fault current, usually something over 20 A, circulates in the fault loop, and the impedance of the loop is calculated within the instrument. I was just wondering if anyone had had any experience of this creating a problem that might explain the reason for the appearance of 400v between L&N. Not sure why the criticism on posing the question?

There's no way using a tester in the manner it was designed can alter the characteristics of a circuit such that 400v appears where you'd normally get 230v.


And if you are finding more examples of dangerous practices and the owner has warned you not tolook too hard, it begs the question should the installation still be in use by anyone, other that a tester, untill found to be completely safe?
 
I agree totally, the factory is closed at the moment due to Christmas and there is only myself & a colleague in the premises. I don’t think I have any powers to enforce the closure of the factory until in a safe condition. I can only submit a report to the “responsible person” emphasising the fact.
 
Last edited by a moderator:

Reply to 400V between L&N in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
642
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
961

Similar threads

Induced voltage can be a bit of a red herring when using DVM my guess is somethings moist.
Replies
5
Views
554
TerryBNZ
T
Very technical :D
    • Like
Replies
9
Views
567

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top