E

Ely Sparks

Hi,

Hopefully someone can help me with the following:-

Having recently carried out a Inspection on a installation I came across the following problem-

After isolating a ring main at the RCBO, I still have approx 40v at the socket outlets. There is another ring main, where after isolating that circuit, the 40v clears at socket outlets. I assumed it was something like a shared neutral between the circuits, but after checking for continuity on the neutral between the two separate rings, they don't seem to be interconnected.

My Megger 1552 won't carry out a No Trip Zs test or RCD test on the socket circuits either, I'm assuming it's related to the above problem. My tester is fine, I checked it on another installation.

Any advice to point me in the right direction of solving the problem would be appreciated.

Thanks.
 
try the Zstest with the other circuit isolated. try measuring the 40v with an analogue meter. this should tell you whether it's an induced voltage or if there's a problem. OH, and double check connections esp. the earthing and bonding.
 
Sounds like a single pole rcbo. ( have a look at the diagram on it ) and a leakage on the other ring final circuit.
Also it the touch voltage is too high your megger will not test. So id check your Earthing conductor.
 
try disconnecting the cables from the breaker and neutral bar. this would highlight induced voltages as the course, if your IR test has proved that the circuits are not interconnected. Also test the MCB, with cables removed, just to be sure its not faulty.
 

Reply to 40v on circuit after isolating at the RCBO. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
309
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
832
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
930

Similar threads

Yup will do exactly that when I'm back down there. Thanks for the help
Replies
6
Views
380
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
447

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top