Hi.

What it means is, to check the effectiveness and compliance of supplementary bonding, total resistance (R) between exposed and extraneous conductive parts must not exceed the calculation of 50/the mA rating of the associated RCD.

I.e, 50/0.03 = 1667ohms.

Where there is no RCD protection then the current causing the fuse/MCB to disconnect in 5s is used instead of the RCD rating.


Bathrooms would be one example whereby supp bonding may now be ommited if ALL circuits within that bathroom are protected by a 30mA RCD.
 
Last edited by a moderator:
tell you what lenny is the man he knows every thing only been on this site for bout a week and he has helped a lot along with a few others cheers
 
nobody's opinions should be discounted on here though. As one of my tutors said there is a lot of engineering judgement needed in electrical works.
Anyone can interpret a regulation right or wrong and thats why these forums are so good for opinions.
 

Reply to 415.2.2 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
545
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
988
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
919

Similar threads

Hello, Is anybody aware of any UK groups or organisations that volunteer or subsidise trades people to do work for; Low income/Vulnerable/Needy...
Replies
0
Views
166
If the socket is installed in a safe place that's fine - you can't influence what people will plug in in the future.
Replies
5
Views
515

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top