Hi Guys

I recently installed a supply to a 45kW motor for cooling tower.

I carried out the following calculation:

IL=P/VLx1.73
=45000/400x1.73
=45000/692
=65.02A

There was only a short run from the cabinet to the motor so a 16mm SWA seemed the correct cable

After the motor was running I checked the current on each phase and found

L1 - 61A
L2 - 81A
L3 - 67A

Does anyone have an explaination as to why there would be so much more current being drawn through L2?
 
Have you checked the windings? Before commissioning a motor, I think it's a good idea to megger the windings, and measure their resistance. This can then be used as a benchmark to test against. What's your Uo on each phase?
 
Also mate, how is the motor started? If its DOL and maybe subject to frequent starting, then you should multiply your Iz by 1.4 to compensate. If its VSD, then manufacturers guidance should be followed due to the wide range of frequencies.
 
Thanks for the advice johnboy, I'm on site tomorrow so will check those points, I need to check the Uo and I haven't checked the resistance of the windings.
 
Check the voltage at the motor for imbalance, (motor running). If the voltage is out of balance it points to the supply / starter. Balanced, check the motor coils for equal CR.

Quick way to find which direction to look.
 
Hi,
Is it star or delta connected? I would suggest using a 3 phase power analyzer such as a fluke 434/ 435 to measure the harmonics at startup and running. The hire is not cheap, but is less than even weeks electricity for that fan...
 
Why hire equipment when basic tests haven’t been reported back?

There will be harmonics at start up no matter what method is used, what are you going to do about them? They don’t affect normal running.

Without knowing the basics what good is a load of globally gook from a condition monitor going to prove?
PF will be haywire, 5
[SUP]th[/SUP], 7[SUP]th[/SUP], 11[SUP]th[/SUP], 13[SUP]th[/SUP] and 17[SUP]th[/SUP] harmonics will be high, that’s a normal motor start up!

We need basic steady running readings first to make a reasoned decision.
 
Last edited by a moderator:
The point is that there is something odd going on here with a very expensive bit of kit. If the windings do have the correct resistance then there could be a supply issue and need to identify what is going on. As for gobbdly gook, the unit is a three phase scope that can measure voltage and current and so again will help to point the finger.
 
There’s nothing “odd” going on, there is a fundamental fault. I don’t ask someone to take readings without reason.

As for the condition monitor:
I know what the kit is, I’ve used it on far larger bits of kit.

Back to my original statement, take basic readings first, don’t muddy the waters with a load of rubbish that isn’t needed. It’s a common failing now, information overload and then neglect the fundamentals of a situation.
 

Reply to 45kW Motor Calc in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Thanks :) Yes, of course, a 3P MCB... just didn't get the terminology correct. Many thanks for the reply
Replies
2
Views
1K
  • Question
Ok Dave thanks, no more accidents yet 🙏😂….
    • Like
    • Informative
    • Winner
Replies
6
Views
2K
There's no reason there to spend the extra. The advantages of a combined cable are neatness and speed of installation.
Replies
10
Views
5K
davesparks
D
  • Question
Yes and also to see if there is a live conductor to earth fault, which would not be shown up immediately if the circuit has no rcd - say motor...
Replies
9
Views
2K
  • Question
Welcome to the forum if you are interested in joining the Trainee section follow this link...
Replies
7
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks