Changed a CU today and noticed the kitchen sockets were wired in 4mm t&e surface mounted in trunking and on a 32A breaker. Now, the CCC for this is strictly only 30A (ref.method B). Would anyone be overly bothered about this? Common sense tells me that it is unlikely this cable will be asked to carry these sort of loads, and any loads will be intermittent as the sockets are counter-top general use sockets, i.e. no heavy fixed loads.
 
It is a situation I would be prepared to leave in place if there are no signs of damage (although in a kitchen it is probably a bit close).
Any over current would need to be between 30 and 32A on a constant basis to be a problem.
However I would not design a circuit like this.
I think the limitations on 32A socket radials in terms of the CCC of 4mm² are often overlooked and it is seen as a standard and easy circuit to install.
 
It is a situation I would be prepared to leave in place if there are no signs of damage (although in a kitchen it is probably a bit close).
Any over current would need to be between 30 and 32A on a constant basis to be a problem.
However I would not design a circuit like this.
I think the limitations on 32A socket radials in terms of the CCC of 4mm² are often overlooked and it is seen as a standard and easy circuit to install.
I totally agree. I often find sparks stating 4mm radials on a 32 OCPD are the best thing since sliced bread but as you say the limitations are often over looked and they don't want to hear it when you point them out.
 
True, I certainly wouldn't install it like this either. But as its already there, I didn't flag it as an issue with the homeowners. There were several other more pressing issues, like downlights covered in insulation and running 50w halogens!
 
Changed a CU today and noticed the kitchen sockets were wired in 4mm t&e surface mounted in trunking and on a 32A breaker. Now, the CCC for this is strictly only 30A (ref.method B). Would anyone be overly bothered about this? Common sense tells me that it is unlikely this cable will be asked to carry these sort of loads, and any loads will be intermittent as the sockets are counter-top general use sockets, i.e. no heavy fixed loads.
I would be bothered about it yes.
 

Reply to 4mm 32a Radial In Trunking in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
317
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
842
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
965

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top