Hello Can I just confirm that if 90 degree cable is used in switch gear that is only ratted at 70 degrees then you use the 70 degree tables to find the maximum current carrying capacity in this case Table 4D1A
I ask this as I carried out an EICR and found 4mm 6491B cable run in trunking supplying 3 phase 32amp socket outlets protected by 32amp Type C Hager MCB
Table 4E1A (90 Degree singles) 37amps
Table 4D1A (70 Degreee single) 28 amps
I did Speak to Hager to try and find the operating temperature of their equipment and they informed me that the MCB are designed to operate correctly at a temperature of 30 degrees if the temperature is any higher then the mcb will operate at a lower ampage ,just confused me more , So tried NIC Tech who just referred me to the tables so no joy there either.
My thinking is the MCB are overatted for the cable
At the moment some supply fork lift chargers with a max current of 20 amp other sockets are not in use, so could be used for anything .
I am looking at given them a Code 2 ( over ratted MCB for cable size , Just wanted to confirm I am using the correct table and the person who designed it didn't.