Hello Can I just confirm that if 90 degree cable is used in switch gear that is only ratted at 70 degrees then you use the 70 degree tables to find the maximum current carrying capacity in this case Table 4D1A

I ask this as I carried out an EICR and found 4mm 6491B cable run in trunking supplying 3 phase 32amp socket outlets protected by 32amp Type C Hager MCB

Table 4E1A (90 Degree singles) 37amps

Table 4D1A (70 Degreee single) 28 amps

I did Speak to Hager to try and find the operating temperature of their equipment and they informed me that the MCB are designed to operate correctly at a temperature of 30 degrees if the temperature is any higher then the mcb will operate at a lower ampage ,just confused me more , So tried NIC Tech who just referred me to the tables so no joy there either.

My thinking is the MCB are overatted for the cable
At the moment some supply fork lift chargers with a max current of 20 amp other sockets are not in use, so could be used for anything .
I am looking at given them a Code 2 ( over ratted MCB for cable size , Just wanted to confirm I am using the correct table and the person who designed it didn't.
 
Hello Can I just confirm that if 90 degree cable is used in switch gear that is only ratted at 70 degrees then you use the 70 degree tables to find the maximum current carrying capacity in this case Table 4D1A

I ask this as I carried out an EICR and found 4mm 6491B cable run in trunking supplying 3 phase 32amp socket outlets protected by 32amp Type C Hager MCB

Table 4E1A (90 Degree singles) 37amps

Table 4D1A (70 Degreee single) 28 amps

I did Speak to Hager to try and find the operating temperature of their equipment and they informed me that the MCB are designed to operate correctly at a temperature of 30 degrees if the temperature is any higher then the mcb will operate at a lower ampage ,just confused me more , So tried NIC Tech who just referred me to the tables so no joy there either.

My thinking is the MCB are overatted for the cable
At the moment some supply fork lift chargers with a max current of 20 amp other sockets are not in use, so could be used for anything .
I am looking at given them a Code 2 ( over ratted MCB for cable size , Just wanted to confirm I am using the correct table and the person who designed it didn't.
NIC being helpful again then?
 
This is a grey area because where does it say that if the conductors are operating at their full ccc, which is a bad idea anyway that the conductors will be at 90°C. Just because the insulation is rated to this temperature does not mean to say that at full ccc it will be at this temperature. Lets face it what current needs to be flowing for the copper to be at 90°C. The improved temperature rating of the insulation allows for increased ccc, that is the whole point of it that it doesn't break down under increased temperature.
 
Ain't it said in note (1) of each Table for 90'C?
It does indeed but I gave never bought into that. The OP has a 32A device, even running at 32A are those conductors likely to achieve 90°C so why bother derating them I find it pointless.
 
It does indeed but I gave never bought into that. The OP has a 32A device, even running at 32A are those conductors likely to achieve 90°C so why bother derating them I find it pointless.
This was my thinking if the circuit was running at 32amp i bet the 4mm cable would only be warm not any were near 70 decrees let alone 90 degrees , and this is why i came on here to see what you guys think , i went for code 2 due to the over ratted mcb if you go by to 70 degree table , but then im thinking is it realy protential dangerous, just to add this installation is 5 years old but looks like it was installed yesrterday , and i feel bad giving it a code 2 , it more to cover my arse if somone plugs a 32amp load into one of the sockets and the terminals over heat which i dont think will hapen but the regs says it will
 
I wouldn't Code it at all. What will happen if someone plugs in a 32A load, does everything heat up to 90°C, never going to happen for it to reach that temperature the mcb will trip long before.
 
I wouldn't Code it at all. What will happen if someone plugs in a 32A load, does everything heat up to 90°C, never going to happen for it to reach that temperature the mcb will trip long before.
Yes very true as hager did say they the higher the temprature the lower the current required to trip the mcb , things like this make me want the throw the regs book in the bin and use common sense, thinking now to go for a code 3 , afterall it apears to be a reg fail . Just to add The reason that i feel the installtion was not designed correctly as the sub main to the db is a 16mm 4 core pvc swa about 20meter long fed from a 125 amp mccb , I gave tnat a code 2
 
That cable is a waste (in my view) as it is not in a 90C environment. So it's not a good design to use it with that mcb. Whether a design that doesn't conform to regs is a no comment, C3 or C2 I will pass on - as I'm scrambling for my tin hat and heading for the trench...

To Westie's point in #5, afaik the ccc ratings are determined by temperature rise, ie the 90C cable is installed method X with a 30C ambient temp, current Y is passed through it and conductor temp rises to 90C, but no further. Current Y is then ccc. Unless I've misunderstood :) .
 
BS7211 wiring has the advantage of being LSZH which is why it is popular. The temperature rating of a conductor is the maximum it can withstand before the insulation breaks down, because whether BS6004 or BS7211 the conductor size remains constant and it is only the temperature withstand of the insulation which dictates ccc. I still maintain there is no need to consider 90°C switchgear, who designs a general circuit where conductors operate at such a temperature.
 
I think at 6491B is used a lot because thats what the wholesalers stock on the shelf , well every time I have asked for 6491x , they say they only have B .

Wilko I started by putting Info on the report.Then after doing some reading up in the regs , I went to code 2 now I have come here and applied common sense , I going to give it a code 3 ,
 

Reply to 4mm 90 Degree Thermosetting cable on a 32 amp MCB in the Commercial Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
328
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
306
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
366

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
223

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top