Eicr today had a 4mm T+E connected into the bottom of a main switch which went to a separate dB with 1 20amp rcbo. Then swa to a hot tub. That part is fine. What I’m unsure about is the reg I can say that the cables are not ok in the bottom of the main switch. The other dB is only about a ft away from the main one. What’s people’s thoughts on this? I know it’s rough as you like!!
 
My pet hate.....Colour Harmonisation!
3 phase meter change...all grey apart from L3 load which was brown....it was grey when it was finished!
Strange thing is on CT metering all the CT wires and the sense voltage wires are red!
Couldn't agree more. Done a TPN board change a couple of weeks ago, half the blacks neutral, half phase......same with the blues. Despite the passage of time I still struggle to see how a panel of (allegedly) intelligent techies spent weeks debating it and came to the conclusion that was a good idea.
 
The circuit originates from the OCPD (main switch), not the 20a rcbo.

It's a little frustrating because it's one of those grey areas like multiple spurs from 1 single point and not confirming r1+r2 on minor works etc. There is no real documentation clearly outlining it's not right but we all know it's a Badgers arse
 
No I'm saying the circuit originates from the main switch which IMO is inadequate protection. When designing circuits you choose a protective device to protect the entire circuit.
Not necessarily. The regulations permit omission of devices for both fault current and overload current under certain conditions, such as short tails to a DB at the intake. An OCPD on the load side of those tails effectively limits the current on the supply side. The same principle allows an unfused spur from a 32a RFC when effectively the CCC of the 2.5mm is around 26a. The fact that only one twin socket is permitted means only 2x13a=26a can be drawn.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Steve93

Trainee
-
Joined
Location
Southampton

Thread Information

Title
4mm cable into the bottom of main switch.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
46
Unsolved
--

Advert

Thread statistics

Created
Steve93,
Last reply from
Deleted member 9648,
Replies
46
Views
5,539

Advert

Back
Top