I know this has been around but how is it reconciled that 4mm in plaster (with or without capping) can be used with 32A MCB when tables say cable rating is less than 32A?
Also:
I can't get my head around why a single socket spur on a single socket spur on ring is different to one double socket spur on a ring which is allowed. Surely two kettles in each arrangement would draw 26A down spur 21 cable?
Thanks.
Craig
Also:
I can't get my head around why a single socket spur on a single socket spur on ring is different to one double socket spur on a ring which is allowed. Surely two kettles in each arrangement would draw 26A down spur 21 cable?