Hi guys was testing a board this morning and it had a 4mm radial circuit protected by a 32a mcb, the circuit came from the d/b and ran through metal trunking in the ceiling and then went into conduit and down inside a wall space ( not sore if insulated or not ), and then into dado trunking, regs state 4mm singles ccc is 32a in trunking ON a wall and then drops to around 26/27a (off the top of my head) when it's in conduit inside an insulated wall. Would use guys put this is a fault and recommend smaller mcb?

just another quick question there was a lug damaged on a double socket back box and the socket was obviously hanging loose, I marked this as a C2 fault but there was few other socket faces cracked but not broken and I was stalling wether it would by C2 or C3? Would u guys like all/any damaged sockets/switchgear replaced before a satisfactory report is given.

thanks guys
 
ESC gives a code 1 for badly damaged accessory`s.
Were there any other circuits within the trunking/conduit, what is the circuit being used for, have you clamped it to see what it is drawing current wise, what is the ambient temperature, are you carrying out an EICR?
 
Installation methods mentioned will indeed derate 4mm to below 32a. If for EICR then probably a code 3, especially if it's a general use socket circuit, and advise swap to 20/25a breaker. If it is supplying something approaching CCC of cable for long periods, then code 2. Just my view!
 

Reply to 4mm protected by 32a mcb in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
321
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
848
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
971

Similar threads

I don't really know if he is or not, but I would have thought an electrician would be able to calculate cable size or know about requirements for...
Replies
8
Views
503
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top