Go easy I’m new to this but.. I’ve just come across a 4mm radial (garage) being fed from downstairs 32A MCB ring. Trying to locate the connection but question is does this comply with BS7671? I can’t tell if it’s on a 13A FS or not at the moment.
Thanks Spoon, I did think that was the case just can’t located the connection at this stage. It has 4 double sockets supplying basic equipment such as fridge etc. I guess 1.5mm would have been ok. I’ve heard the term “lollop circuit” used before but this would usually be the other way round i.e 4mm to 2.5. Next step find connection and if not in a FCU then either 1. Put one in or 2. Run 4mm back to CU on 20A OCPD.
(I also don’t really like 1.5 feeding 13a sockets Just my opinion)
Thanks Spoon, I did think that was the case just can’t located the connection at this stage. It has 4 double sockets supplying basic equipment such as fridge etc. I guess 1.5mm would have been ok. I’ve heard the term “lollop circuit” used before but this would usually be the other way round i.e 4mm to 2.5.
Next step find connection and if not in a FCU then either 1. Put one in or 2. Run 4mm back to CU on 20A OCPD.
Interesting discussion. I have wondered whether this arrangement could be safe or not. A couple of thoughts:However, the situation you describe - 32A OCPD --> 2.5mm ring --> 4mm spur --> several sockets - could lead to overloading, depending on where on the ring the 4mm spur is taken from. If it's on the middle of the ring (roughly equal resistances from the spur point back to the board) then no problem: the maximum current (32A) will be fine on the 4mm, and be split more or less equally down both legs of the 2.5mm ring. But if the 4mm spur is close to one end of the ring (i.e. relatively close to the DB), then the majority of the current will go down the short leg, overloading one leg of the 2.5mm ring.
Reply to the thread, titled "4mm radial from 2.5mm ring on 32A?" which is posted in UK Electrical Forum on Electricians Forums.