HappyHippyDad

-
Esteemed
Arms
Supporter
Joined
Dec 18, 2011
Messages
5,320
Reaction score
6,561
Location
Gloucestershire
Bit bored, boys in bed, beers in tummy and I thought I'd ask everyone why a 4mm radial is allowed to have a 32A MCB protecting it when its current carrying capacity is only above 32A when it is clipped direct or in free air?

I'm thinking diversity, but what if its your only circuit for sockets, then no diversity applies and I kind of assumed diversity was for max demand of household anyway?

Cheers :thinking:

ps... may be a little sporadic replying as just starting Star Trek!!
 
Bit bored, boys in bed, beers in tummy and I thought I'd ask everyone why a 4mm radial is allowed to have a 32A MCB protecting it when its current carrying capacity is only above 32A when it is clipped direct or in free air?

I'm thinking diversity, but what if its your only circuit for sockets, then no diversity applies and I kind of assumed diversity was for max demand of household anyway?

Cheers :thinking:

ps... may be a little sporadic replying as just starting Star Trek!!

To boredly go where no man has gone before, eh?
 
IMO if the 4mm is to be derated due to insulation, whereby it's CCC is reduced below 32A, then a lower rated MCB should be used. generally, 4mm radial would be clipped direct and maybe partly buried in masonry, so a 32A would then be suitable.
 
Because it says so in Appendix 15. So it must be right?!

I think you're probably saying that a bit tongue in cheek:D. Appendix 15 does say that, so I thought I must be missing something as BS7671 is pretty thorough and precise. I guess this is where I'm reminded that BS7671 is not infallable and common sense and knowledge should be used as well.
 
It's true 4mm radials are just teetering on the edge when it comes to CCC on a 32a breaker. It's one of their limitations, and probably why the ring is still so popular! My kitchen radial is on a 25a breaker due to installation method. I also find 4mm T&E a bit limiting on occasion when it comes to max circuit length....would be so much more useful if it had a 2.5mm CPC.
 
It's true 4mm radials are just teetering on the edge when it comes to CCC on a 32a breaker. It's one of their limitations, and probably why the ring is still so popular! My kitchen radial is on a 25a breaker due to installation method. I also find 4mm T&E a bit limiting on occasion when it comes to max circuit length....would be so much more useful if it had a 2.5mm CPC.

Agreed a 2.5mm CPC would be very useful.
 
IMO, BS7671 has got the figures wrong. 2.5mm is rated at 27A (method C). 4mm is almost double the csa of 2.5mm) and is also stranded cable, so should be rated accordingly. a rating of 40A ( method C) would be more appropriate. tin hat on.
 
Only for fault protection to bring Zs down, but if covered by RCD then no problem, if it has 4.5mm conductors even better! Tin hat on.

That was the whole point. Why else would I mention having a bigger CPC? To make it easier to strip the cable??? :)

And are you suggesting that we should ignore the disconnection times for the fuse or breaker if an RCD is present? So if we use an RCD then we can have circuits as long as we want them? :)
 

Reply to 4mm radial on a 32A? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
521
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top