Well I feel like I am about to get shot down in flames just like Jessie James, but my point was that if the circuit supplies fuse spur outlets then whatever is conected to them is fixed equipment rather than portable, and does'nt need to disconect within 0.4 seconds !
The possability of any other equipment being plugged in and used elsewhere is removed !
As they said at Rouke's Drift, "fire at will" !!
ah, can see the way you are going, you mean a switched fuse 'flex' outlet, rather than a s/o?
bit of a faff just to avoid RCD's! But of course, thats assuming the RCD was being provided for supplemetanry protection because the circuit failed to achieve its disconnection time, which just changing it to 5s is a bit of a kop out......
'course under the 17th this wouldnt apply anyway, because now its down to CPD size not circuit supplied (submains excluded!)
doing it under 16th it doesnt need an RCD, and under the 17th the sockets wouldnt need RCD if they are labelled 'lottery machines only' (although the cables supplying still might)
i doubt the client would want to call an electrician everytime he wants to shift the lotto m/c so fu spurs is a non starterI have been asked to run a new circuit into a shop for a new lottery machine. Chap wants 3 x double metal clad sockets. I was thinking of running a 4mm t&e radial supply over 15 meters. What size MCB would I be advised to put into the CU?