Is there a problem using two 4mm radials in a kitchen using the same mcb as opposed to a 2.5mm ring?

Thanks.
 
yeah why use the same mcb? i dont see the advantage of two radials on the same mcb as opposed to a ring main. if a fault develops the whole kitchen will go off. plus anyone else looking into the cu will maybe think it is supposed to be a ring
 
Reg 431.1.1 states:- detection of overcurrent shall be provided for "all line conductors" and shall cause the disconnection of "the conductor" in which the overcurrent is detected, but not the disconnection of the other line conductors..... 2 radials = 2 mcbs. Safe practice, no confusion for the next sparky looking in the cu and everyone is happy. Kitchen, rcd x 2 maybe?
 
Last edited:
Reg 431.1.1 states:- detection of overcurrent shall be provided for "all line conductors" and shall cause the disconnection of "the conductor" in which the overcurrent is detected, but not the disconnection of the other line conductors..... 2 radials = 2 mcbs. Safe practice, no confusion for the next sparky looking in the cu and everyone is happy. Kitchen, rcd x 2 maybe?

Paul, take a look at App. 15 in the BRB at the 4mm² radial. As long as you use 4mm² T&E you can spur off to more than one socket.

The picture shows it being spurred off a double socket outlet, which IMO is no different to spurring straight off the OPD.

However, I agree with the above. I can't see why anyone would want to do it this way as opposed to a ring circuit. :confused:
 
Agree with appx 15 that's spurring from the circuit not the mcb. OSG appx 8 says it is ok to spur from the cu but only one single or double socket. It would be good to have more info, is the kitchen an awkward layout?
 
Hi, sorry for delay in replying - refurb job and working all hours.

I went down the ring main route in the end. The question was asked due to the lack of space for cables in the existing run and didnt want to "loop back" to other side of the kitchen.

Thanks for all the replies.
 
Further to what has been said above if I came at a later date and saw 2 x 4mm out off same breaker I would assume it was a ring and when testing for ring continuity and not find any I would start looking for the break in the ring.
 

Reply to 4mm radials in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
507
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
2K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
807
Thanks for all the replies. So they’re just moving in and need more, it’s going to their room to charge phones , and lamps so not loads of power...
Replies
9
Views
456

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top