5 second disconnection time | on ElectriciansForums

Discuss 5 second disconnection time in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Joined
Feb 24, 2010
Messages
992
Reaction score
126
Location
South east
Just a quickie to refresh my memory.

TN system disconnection times.

Final circuits not exceeding 32 Amps.
230V 0.4 seconds. (table 41.1 page 46 BRB)

Final circuits exceeding 32 Amps IE fixed equipment and distribution circuits.
230V 5 seconds.

RCD's are used for socket outlets not exceeding 20 Amps and mobile equipment with a current rating
not exceeding 32 Amps for use outdoors.

Just clarifying.
Is this correct, are there any more, any exceptions?
Thanks.
 
Any final circuit in a special location as it has to have RCD protection. so 0.4s at 150ma

Street lighting as every light has individual fuse
 
Last edited:
RCD's are used for socket outlets not exceeding 20 Amps and mobile equipment with a current rating
not exceeding 32 Amps for use outdoors.

Exceptions to socket outlets being:
1/ Under the supervision of a trained/skilled person
2/ Specific item of equipment that would benefit from not being RCD protected
 
What I can't understand is that in the back of GN3 page 108-110 there are tables with a selection of fuses. BS3036, BS88, BS1361.

These tables are split into two parts, one being 0.4 second disconnection time and the other being 5 seconds disconnection time.

If we look at table 41.4 page 108 it lists BS 3036 with 5 second disconnection times and starts at 20 Amp fuses, where would a 20 Amp fuse be used for a circuit with a disconnection time of 5 seconds.
These tables seem to be in contravention to BS 7671.
I don't understand.

Also there are tables for BS 88 fuses with 5 second disconnection time starting at 20 Amps and BS 1361 fuses with 5 second disconnection times starting at 20 Amps.

So according to these tables there are instances where you would put a 20 Amp fuse in a circuit with a disconnection time of 5 seconds.

I'm confused, help. :dozey:
 
If you relate the disconnection time to the time current curves in appendix 3 that will show that on a 5 sec disconnection time you are allowed highter Zs values. so the 5 sec Zs is higher then 0.4 values

lower the value =higher PSC = Faster disconnection


In a street lighting circuit you can use HRC fuses for a 5 sec disconnection time.
 
Last edited:
There are still many installation distribution boards (industrial) that have mixed disconnection times and for smaller fused circuits such as lathes and other fixed industrial machinery combined with socket outlets.
 
i would use it as the street lamp supply yes. remember that street lights have individual fuses therefore the supply could be classed as sub main distribution.
 

Reply to 5 second disconnection time in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
351
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
899
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

The challenge that you have with this is that you've no confirmed start point. Because you have a lack of an EICR you don't actually know what...
Replies
7
Views
593

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top