Have been asked to look at a 500m run for a 10kW and 50kW PV options. I'm getting catastrophic VD losses on the 50kW in AC TPN on 35mm SWA. For the 50kw you’re looking at 13% losses with 35mm. That’s over 6kw lost.
The losses on the 10kw AC TPN are 1.5% on 35mm which i'd consider on that basis but thats still £5K ish of cable which looks pretty damn pricey for 10k of PV.
Any ideas?
The losses on the 10kw AC TPN are 1.5% on 35mm which i'd consider on that basis but thats still £5K ish of cable which looks pretty damn pricey for 10k of PV.
Any ideas?