O

ohlins

Hey guys quick test for you.I bolloxed my apprentice today, he was doing zs test and the tester came up with the above reading L 186V N 40 odd he had no idea what the fault could be (has passed all test mods at colledge).Do i expect too much of him?.Prize for 1st right answers!!.
 
This occurs when the N-E impedance becomes significant causing a voltage drop. The actual voltage drop becomes supply load dependant, which can lead to variable test results and seemingly unpredictable behavior at the installation e.g. apparently random tripping of RCDs.
On a TN-S or TT system a small potential above earth is virtually inevitable due to all the consumer loads sharing that supply N.
On a TN-S system a significant potential may occur if the outer sheath or armouring of the supply cable or their connections become eroded or corroded.
On a TT system lack of a local earth or poor earth electrode or connections to it.
On a TN-C-S system the most likely cause of this fault is a voltage drop along the PEN conductor caused by faulty connections to earth electrode(s) or eroded earth electrode(s) on the DNOs PME network.
 
Last edited by a moderator:

Reply to 50v on neutral tester wont test in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
264
Hi all, We have a limited in house PAT testing requirement and were advised that the TIS700 fitted our needs. The unit works fine for 110V and...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top