Following a query in another post with a respected member about the suitability of pvc concentric cable for underground wiring, I wrote yesterday to the respected author John Whitfield, who has written widely on the subject of the IEE Wiring regulations, his most notable work probably The Electricians Guide by EPA Press.
I noted that both his work and an NICEIC C&G 17th guide listed concentric cable as being suitable for underground use, without constraints, simply by being concentric in construction.
I asked:
1 Does the acceptability of concentric use, lie in the interpretation of 'metal sheath suitable for use as a protective conductor' in 522.8.10?
2 Does Concentric layer: Neutral conductor & an uninsulated CPC count, or does the outer layer need to be a continuous sheath?
522.8.10 a cable buried in the ground shall incorporate an earthed armour or metal sheath or both, suitable for use as a protective conductor.
522.8.10 does not specify that concentric construction alone would satisfy BS7671
Mr Whitfield has kindly replied by return (I have paraphrased the reply):
Having examined your note and BS7671, I am sorry to say that there appears
to be no definitive answer to your question.
BS7671 is, as you have said, silent on the subject. It is really down to
whoever signs the final certificate, but by then it is too late!
For what it’s worth, in my own opinion, a concentric outer cover made up
partly of neutral and partly of protective conductor will comply. BUT I am
not an accepted authority.
I hope that this helps.
If anyone else would like to comment, I would welcome the input, and again I would like to thank Mr Whitfield for taking the trouble to respond.
I noted that both his work and an NICEIC C&G 17th guide listed concentric cable as being suitable for underground use, without constraints, simply by being concentric in construction.
I asked:
1 Does the acceptability of concentric use, lie in the interpretation of 'metal sheath suitable for use as a protective conductor' in 522.8.10?
2 Does Concentric layer: Neutral conductor & an uninsulated CPC count, or does the outer layer need to be a continuous sheath?
522.8.10 a cable buried in the ground shall incorporate an earthed armour or metal sheath or both, suitable for use as a protective conductor.
522.8.10 does not specify that concentric construction alone would satisfy BS7671
Mr Whitfield has kindly replied by return (I have paraphrased the reply):
Having examined your note and BS7671, I am sorry to say that there appears
to be no definitive answer to your question.
BS7671 is, as you have said, silent on the subject. It is really down to
whoever signs the final certificate, but by then it is too late!
For what it’s worth, in my own opinion, a concentric outer cover made up
partly of neutral and partly of protective conductor will comply. BUT I am
not an accepted authority.
I hope that this helps.
If anyone else would like to comment, I would welcome the input, and again I would like to thank Mr Whitfield for taking the trouble to respond.