G

GreggElectrical

I've always stayed away from any of this sort of stuff but I have a very insistent customer. He says he will disconnect the other 4 panels if his fit application is not accepted (yeah right!). He basically has room for 5kw but obviously wants the 16p rate (install in August). Argument is that the system should be limited to 3.68kw by use of a g83 inverter so TIC and DNC should be no more than 4kw. I really cant see this working but wanted to know if anyone has ever tried it and what happened.
 
I have done it on some installations without problem because I believe it is within the legal definition of TIC/DNC. I have also made sure the customer is careful what they write on the FIT application so as not to raise a hare.

However, I have become aware within the last few months of at least a couple of installers who have customers being told by their FIT supplier that TIC = kWp of panels rather than inverter output, thereby placing them in the 4-10kW FIT band rather than the 4kW or less band. Much grumpiness all round!

So if you do it, you and your customer must do so with the prospect that it might be challenged at some stage. And that could result in having to resort to OFGEM complaints process and legal action.
 
Is it a good idea, in one word:

No.


But......

If the panels face North, East or West, or are on a very steep or very flat roof, or suffer severe shading at peak generation time it might be a reasonable combination.

But if the panels are SouthEast, South or SouthWest, in normal conditions of roof slope and minimal shading, the inverter will be seriously overloaded and will probably send the "excess" electricity back round to the panels, causing overheating of the inverter and the panels - and reduction in performance on sunny days (panels drop in performance when hot, and having the "overload" power sent back from the inverter will overheat the panels even more - probably not helping the panel lifespan).

On particularly good days, it's not unusual to see panels outputting 10% more Wattage than their nominal rating. My 250W panels have reached 270W output per panel in ideal conditions. So your client might think he's got peak panel output of 5kW, when it could well reach 5.5kW or more.

Some inverters have a maximum input allowance for the warranty. My Aurora PVI 3.6 has a maximum allowance of 2 strings of 2kWp each, or a single string of 3.75kW. More than that and the warranty is theoretically void.
 
........ the inverter will be seriously overloaded and will probably send the "excess" electricity back round to the panels, causing overheating of the inverter and the panels - and reduction in performance on sunny days (panels drop in performance when hot, and having the "overload" power sent back from the inverter will overheat the panels even more - probably not helping the panel lifespan).........

is a generalisation and not very accurate way of describing what happens to the power flows.

Plug some numbers into Sunny Design and you might be surprised what can be put on the inputs of say a 4000TL.
 
Just to add, if you add more panels and try to keep things quiet, say over 4 KWP and the system performs very well, when the customer sends in his meter reading if it is above what the provider expects (some have already been challenged) then questions will be asked, if the provider/OFGEM, do deem the panels as TIC then should you install 5KW it could be deemed as fraud if they claim the 4KW tariff.

There are many different views on TIC/DNC for PV, and the problem is the forms used are generic for all types of generation, I have looked into this in detail, and had different answers, helpful I know....

My advice would be so stick to 4KWP of panels, but install quality not quantity, or explain the risks to the customer and put all the risk onto them.
But take care, it looks like Barking is doing all he can to destroy this industry..
 
from a technical point of view, yes it's no problem, the system will work really well.

from a FITs point of view... after a long running argument with Ofgem, we've ended up having to remove a panel from a customers system to comply with their current unlawful interpretation of the legislation, that runs contrary to their own published guidance, because we didn't feel in a position to stump up ÂŁ10k to take it to judicial review.

so, if you've got 10-15k to spare to challenge ofgem, then by all means go ahead as the 5kWp array limited to 3.68kW AC output should lawfully be classed in the 0-4kW FIT band (and we've paid for 2 legal opinions on this), but Ofgem's position on this says otherwise, and this is the guidance they've now issued to all FIT suppliers (but refuse to actually issue to MCS installers), which is why most of the FIT forms now expressly ask for the kWp rating of the panels.

so we're now sticking to 4kWp of panels, with gritted teeth, and an intention to sue Ofgem if we ever get our finances in order enough to spare the money to do it.
 
I thought this would be a bit of a mine field so I have always said no before. Only reason this one was tempting is it would be a post July booking and only 1/2 mile from my door. That said, I wont be doing it for him.

I always have seen this as a bit of a cheat. Basically the fit provider is looking at paying for no more that 3500 units at the <4kw rate per year. If everyone could stick on what they like and cap generation at 4.0kw during sunny times we would all have systems producing up to 5000+ units per year. This really would not sit well with ofgem, the fit provider and our beloved Barker. I think in the long run there are not enough people willing to throw cash around in court to make it stick however right they technically are. Which means it could get tricky for those willing to push the envelope on this.

To borrow a phrase from Dragons Den......Sorry but for that reason I'm out!
 
eduction in performance on sunny days (panels drop in performance when hot, and having the "overload" power sent back from the inverter will overheat the panels even more



 
From our studies a single tracker will add about 25% ... Double tracker about 35%

Of course on a tracker he'll need planning permission.

However using good old unistrut a single tracker is very easy to build, a commercial tracker will cost about the same as the extra kWp :)
 
I would ground mount on individual mounts and get the wife to run out every hour and turn all the panels about 15 degrees to earn her keep -only during sunny weather though!
That would be about 3 days in the last 2 months.LOL
 
Keeps her trim :53:
 
(panels drop in performance when hot, and having the "overload" power sent back from the inverter will overheat the panels even more - probably not helping the panel lifespan).

Is this possible? Surely there is no excess energy - just potential energy that isn't realised? Nothing will get sent back through the panels, will it?

Are you sure that Power One Inverters only have a warranty for strings of 2kWp each?
 

Reply to 5kw panels, G83 Inveter, 3.68 TIC. Anyone actually done this? in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
315
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
841
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
954

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top