Flanders

-
Arms
Joined
Jun 28, 2013
Messages
1,659
Reaction score
1,003
Location
Tamworth
Carrying out and EICR on large factory and they have welding plug into 63 amp commando sockets but are protected by 30 amp BS 88 fuses.

Now the regs states Socket outlets with a ratted current not exceeding 32 amp need RCD protection. 411.3.3 (i)

Because the Socket it 63 amp I say it does not need RCD protection because its the ratting of the socket that decides if an RCD is required ,not the over current protective device. So am not going to code this just put it as info on the observations.

Or would you guys Code it ?

Got me thinking though if you wanted to avoid fitting an RCD and don't what to do a risk assessment, just fit a 63 amp plug and socket and protected by a 16 amp MCB , Not sure how you would terminate the 1.5mm flex in the plug though :)
 
Just wondering why it is the ratting of the socket that is so important and not the ratting of the OCPD or have the boys and girls at the IET not thought of this ?
 
I’m also interested in this, we have a movable piece of equipment that is currently on a D16 with 16A MCB and 100mA RCD.
It trips the RCD (it’s in manufacturers documents that it needs a 300mA RCD).
Can I just change it to a 32A socket and remove the RCD?!
 
I’m also interested in this, we have a movable piece of equipment that is currently on a D16 with 16A MCB and 100mA RCD.
It trips the RCD (it’s in manufacturers documents that it needs a 300mA RCD).
Can I just change it to a 32A socket and remove the RCD?!

Why is it on a 100mA RCD if the instructions say a 300mA is needed?
 
I’m also interested in this, we have a movable piece of equipment that is currently on a D16 with 16A MCB and 100mA RCD.
It trips the RCD (it’s in manufacturers documents that it needs a 300mA RCD).
Can I just change it to a 32A socket and remove the RCD?!
No. A 32 amp socket will need a 30ma rcd protection if no risk assessment also as the manufacturers intructions say it needs a 300ma rcd then thats what you should fit, it could be triping the 100ma rcd as this is not suitable for your equipment, have you had the earth leakage tested or does it state in the intructions how much leakage there should be ?
 
It used to run fine on a 100mA RCD.
A mains filter was causing the problem, replaced it and problem went away but then came back. After speaking to manufacturer they said there can be 100mA of earth current (not that it needs 300mA, but I’ll fit one anyway).

Why does a 32A plug need an RCD, I too thought it was sockets of 16A and below?
 
Take a look in the 18th as it's all changed.
 

Reply to 63 amp 3 phase socket protected by a 30 amp fuse RCD? in the Talk Electrician area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

As per above from Dave. Swap to a 63A outlet and problem goes away. What gets plugged into it is not part of an inspection.
Replies
20
Views
2K
  • Question
This is an interesting issue. I agree with you however I took this to task with a scam inspector some years ago and we agreed to disagree that...
2
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top