Have just bought a house but find main supply is only 63amp
Other houses in street seem higher going by street plan I take it the 35 in all other houses and 25 in mine is relevent to this but don't know what it means - picture is from Scottish and southern electric company

anyway 63 is not enough for todays power consumption
All tails seem to be for 100amp and just got smart meter put in this week
southern are sending quote but is it not their responsibility to get an adequate amp to my house
Also the wire coming is white and not the usual grey (better or worse i don't know)
 

Attachments

  • [ElectriciansForums.net] 63amp-100amp
    770CDF28-4AF7-44A8-8EAA-9AF62FDBBF18.jpeg
    152.5 KB · Views: 109
  • [ElectriciansForums.net] 63amp-100amp
    C124F4E0-A43A-4D43-A178-4354FC475429.jpeg
    403.1 KB · Views: 106
Although it is SSE's responsibility to maintain the supply to you once it's there, I don't believe they have a duty to provide a particular rating.

The picture does appear to suggest you have smaller cable running to your house than the surrounding ones, for whatever reason (perhaps yours was built first, or had the main fuse moved at some point and it was cheaper to install a 63A one)

In reality it's very rare for a supplier's fuse to be an issue with overload, simply because most domestic properties use nowhere near that - or only in short term bursts which the fuse can cope with (It will not blow the moment you use more than 63 Amps in load)

It may be worth seeing if they will come out and inspect, they may be able to raise the fuse to 80A even if not 100A.

If you do have a car charger put in, there are ones that can adjust the charge based on the load elsewhere so that it never takes more than the supply can safely give. Since most car charging occurs overnight when other big loads aren't usually on, it may not be a practical issue anyway.
 
TLDR - you'll be fine. 15kw is more than enough for an average small domestic - stop learning by social media ;)
If its fine why are most 100amp and rest of street 35mm wires and mine only 25mm (middle house not first or last built)
P.S Is there anywhere i can find out history of wiring to see if mine has been downgraded or other houses upgraded
 
If its fine why are most 100amp and rest of street 35mm wires and mine only 25mm (middle house not first or last built)
P.S Is there anywhere i can find out history of wiring to see if mine has been downgraded or other houses upgraded
For starters you'll only almost certainly have an incoming cable of 16mm, exactly as all your neighbours will.
Second, just because you've found a diagram online somewhere don't assume it's accurate, it's very common indeed to find 80A fuses in 100A cut-outs.
Thirdly, when the DNO's are working out their own diversity calculations they use a ridiculously low value of something like 1.5KW per dwelling.
Fourthly, you'll probably find that you've been spurred off a neighbour which is common and absolutely fine.
And bringing up the rear at number five..... what on earth makes you think that you are going to be drawing constantly more than 15kW???!! To put that into context your electricity bill would be in excess of ÂŁ23k per year......
 
Hi - you might find if the DNO supply fuse melted due to your domestic load they would attend and upgrade it, free of charge. At least you’d find out why it’s been set that way.
For what it’s worth, I have 60A fuse on the home supply (Bronze Age DNO cable capacity) and it’s never been an issue, but I do have gas heating and no leccie van to charge, yet.
 
For starters you'll only almost certainly have an incoming cable of 16mm, exactly as all your neighbours will.
Second, just because you've found a diagram online somewhere don't assume it's accurate, it's very common indeed to find 80A fuses in 100A cut-outs.
Thirdly, when the DNO's are working out their own diversity calculations they use a ridiculously low value of something like 1.5KW per dwelling.
Fourthly, you'll probably find that you've been spurred off a neighbour which is common and absolutely fine.
And bringing up the rear at number five..... what on earth makes you think that you are going to be drawing constantly more than 15kW???!! To put that into context your electricity bill would be in excess of ÂŁ23k per year......
The drawing was sent yesterday from southern power here is the whole drawing
 

Attachments

  • [ElectriciansForums.net] 63amp-100amp
    6A4E9D08-141D-48FC-B078-CCDCEB3F0760.jpeg
    185.4 KB · Views: 86
I'm only going to respond to this thread once as I can see it's going to roll on for pages and pages and pages.

Don't trust the drawing, it will be from historic records and may not be accurate.
Size of cable does not indicate the size of fuse in a property, the rest may all have 63amp.

Any Eletrician doing work in the house will be able to work out the max demand and check if the fuse and supply is adequate, which as others have already pointed out, it is, even for future demand.

To get the supply upgraded an Electrician will have to supply details of the extra load to convince SSE to allow an upgrade which could cost you thousands if the local network has to be re-enforced.
SSE may say there is no need to upgrade even with the extra load.

There isn't a problem or even a prospective problem.

What about the Gas and Water is there a problem there as well?
 
I'm only going to respond to this thread once as I can see it's going to roll on for pages and pages and pages.
Yeah, but, fish and barrels, fish and barrels...... (can you tell I'm bored already today?)
 

Reply to 63amp-100amp in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top