I

iamelectric

got a job to install a 63amp supply 3 phase commando socket , for a lighting show for an opening night , it was a metre from the D.B so i wired it in 16mm SY cable, i have now been asked to supply am extension cable for it , one male plug one female plug , about 25m long , i was thinking of using 10mm SY for it as its more manageable , but 10mm comes in at 61 amps ccc , is this ok as its an extension?
 
got a job to install a 63amp supply 3 phase commando socket , for a lighting show for an opening night , it was a metre from the D.B so i wired it in 16mm SY cable, i have now been asked to supply am extension cable for it , one male plug one female plug , about 25m long , i was thinking of using 10mm SY for it as its more manageable , but 10mm comes in at 61 amps ccc , is this ok as its an extension?

Why would you think that an extension lead can have a lower ccc than the OCPD protecting it?
 
^^^^ what do u mean i have already installed the socket
As in the 63A socket (and plug) of the extension cable you are creating?

In any case a different sort of regulations apply ... BS7909 and regulation 7.3.3 states:

Cables for use outdoors and in general use should be rubber insulated and
sheathed in accordance with BS 7919 (H07RN-F or equivalent), with a
voltage designation of not less than 450/750 V (heavy duty flexible, as
defined in BS 7540-1) and resistant to abrasion and water.

NOTE 2 Thermoplastic cables are not designed for use outdoors. For example,
cables known as ‘arctic blue’, ‘SY’ are thermoplastic and are not suitable for use
outdoors.
 
got a job to install a 63amp supply 3 phase commando socket , for a lighting show for an opening night , it was a metre from the D.B so i wired it in 16mm SY cable, i have now been asked to supply am extension cable for it , one male plug one female plug , about 25m long , i was thinking of using 10mm SY for it as its more manageable , but 10mm comes in at 61 amps ccc , is this ok as its an extension?
16mm 3 core H07-RNF ... nice n easy :)
 

Reply to 63amp extension lead in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
348
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
886
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

They do a cy type with pur coating and it is even tougher but is shielded
Replies
3
Views
400
It's a room where someone sleeps, so it's a bedroom. Minimum standards were set in the Parker Morris report in around 1963. Anything built after...
Replies
5
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top