I know my mate the engineer and his dislike of the "rod". but in this case as the bungalow is 65 mteres away I would be definately looking at making this installation have it's own equipotential zone.
As with Yellowvanman I would be thinknig about a 2 core SWA and untilising the SWA as the CPC. If you do rod the bungalow then the CU earth bar would be that installations MET.
What is the house earthing system ? If it is TN then I would fit a Fuse Isolator/MCB enclosure to protect the SWA, a 60/50amap fuse for that install should be ample, in all honesty you could get away with a BS 88 50amp if your calcs show that 25mm is nearly on the threshold. You can even think about a 50amp MCB as well. Then disregard the TN at the garage CU.
If your house is already a TT then you need to RCD protect the SWA with a 100mA S type RCD for that SWA as the chances of you getting a good enough Zs for disconnection is slim.
At the Bungalow I would fit
2 X A3 20 amp radials
1 X 6amp light, I would also think about putting a couple of emergency lights in, as 65 mts from the house, and the lights fail can be disconcerting.
45amp shower
So 50/60amp supply would be fine. I would also use RCBO's rather than a split board, IMO much better.
Finally I would also run out telephone/data and perhaps TV, as once you have dug 65 mts your not going to want to dig it again.