Hi Everyone,I Have Been Called Out To A Job With A Problem On The Lighting Circuit. Couldnt Spend Too Much Time On It As It Was Last Thing Today (Friday) The Breaker Holds In For Approx 5mins And Then Trips, When Tested I Found It Had A Short Between Phase/Earth AND Phase/Neutral, Surely A Short Circuit Would Take The Trip Out Straight Away And Wouldnt Not Hold In. I Cant Think Of What The Problem Is...........Help lol
yeah all lamps were removed and yeah i did do that first lol. im stumped, anyways traced the wire back to a JB, was the switch wire for the kitchen in the end, took it out and replaced it with a new cable. still not sure what the fault was as the wire went under her bathroom, so i found a new and easier route with my cable back to the switch. thanks anyways
If you used an IR tester to ascertain the "dead short" then alarm bells should have started ringing as to why the time delay to disconnect.
Continuity of CPC. R2 test on that circuit. Main earth bonding/earth loop all contribute to the disconnection time.
Reply to 6amp MCB Trips After 5 Mins :-S in the Australia area at ElectriciansForums.net
Its important to remember that a plug top fuse is just a rewireable fuse that's convenient to change and shouldn't be confused with a HRC fuse...
I fitted a Mem MR30 Pod and MCB, about ÂŁ75 for both.