I'm fitting two replacement sub-mains panels as part of a long-term upgrade from split-phase to three phase on a part-domestic part-commercial site (my own gaff). I'm using all RCBOs because I like them, but am less keen on the cost of the commercial variants ...
Fellow spark says one MUST use 10kA breakers in a TP board because it's commercial kit. I say rubbish, so long as 6kA-rated devices physically fit and the fly leads are long enough (Hager's are) and as the Potential Fault Currents are nowhere near 6kA anyway (at the end of long SWA runs), 6kA units are technically fine.
Am I missing anything?
Fellow spark says one MUST use 10kA breakers in a TP board because it's commercial kit. I say rubbish, so long as 6kA-rated devices physically fit and the fly leads are long enough (Hager's are) and as the Potential Fault Currents are nowhere near 6kA anyway (at the end of long SWA runs), 6kA units are technically fine.
Am I missing anything?