6kw sauna sharing cooker supply is it even a possibility?? | on ElectriciansForums
Discuss 6kw sauna sharing cooker supply is it even a possibility?? in the UK Electrical Forum area at ElectriciansForums.net
London
Right this maybe a completely stupid idea....but, guy wants a 6kw pre built sauna in back garden. The fuseboard million miles to back of house so wiring new circuit would be a nightmare. But he does have a cooker supply right near back door of garden. I know it's deemed good practice to have cooker and sauna on own dedicated circuits but if come from cooker switch with adequate sized cable out to rotary switch for sauna and they was never used at same time could this not be a possibility? I have also heard mentioned before that in scenario like this a change over switch might be able to be used? And this would prevent both being used at same time. Could someone explain to me how this would work and how it would be installed. Thanks
no it can not be done, considering the loading.think about the loading.
Is the cooker on an RCD circuit?
Also what sort of distances and what cable is already in place? You need to check the voltage drop even though a change over switch would avoid the risk of cooker and sauna at the same time.
Does the sauna have lights? It might be a risk if someone changes back to use the cooker with folk in there. I'm not seeing this as a terribly good idea.
I will also say no this is not a good idea. It is bad practice to design a circuit with fixed loads that exceed the rating of the circuit.
You can't rely on a customer to ensure that.
A cooker switch is unlikely to be designed to accommodate 2 cables per terminal.
Would a shower priority relay do the job? It's rough as far as functionality goes - people wouldn't expect to have two seemingly unrelated things interlocked - but would solve the electrical objections.
The DB is rcd protected mate. The cooker is on 6mm and would say at most 10 metres in length. I would extend this in 4mm in swa to outside waterproof rotary switch. This additional length would be around 5 metres
[automerge]1586463267[/automerge]
[automerge]1586463460[/automerge]
Yeah very true Freddo ?
[automerge]1586463629[/automerge]
Have you got a link or description of these Lucien and how they could potentially be used. Thanks
As above priority switch but I don’t think it’s something I’d want to be involved in....you mentioned 10 mtrs and 5 mtrs is that all the distance is to the consumer unit?...doesn’t seem far are you sure there’s no way to run a dedicated circuit? Outside building etc?
Is there an other reason for not running in a new circuit (e.g. no free slots in CU)?
That would be best solution. A quick search for shower priority units pulls up a few in the ÂŁ100 region, but its not a great solution as you also have to reset cooker clocks, etc, after every operation, etc.
Depending on how it is enclosed/insulated 6mm T&E won't be suitable for 48A
But checking and/or replacing with 10mm would allow something like a 50A MCB at the CU if a lack of space is the reason for not running another circuit.
Reply to 6kw sauna sharing cooker supply is it even a possibility?? in the UK Electrical Forum area at ElectriciansForums.net
Hello oscar21, When I wrote about cables heating up I meant that IF a cable heated up that heat could not dissipate correctly if the cable was...
Thanks davesparks. Looking at the diagram on the driver that's what I interpreted too, but I heard somewhere that the DALI system doesn't like...