6mm cable 40amp breaker. 8.5kw shower | on ElectriciansForums

Discuss 6mm cable 40amp breaker. 8.5kw shower in the Australia area at ElectriciansForums.net

H

highspark

Did a condition report today found an 8.5kw shower on 40 amp breaker with 6mm cable. It's ran through wooden box section from fuseboard to bathroom so in free air but I then thinks its been chasedinto the wall as it enters the bathroom. Do you think this requires a code?
 
With teletrix. Definition says. Where the cable is fixed or embedded in a masonry wall the current carrying capacity may be higher. Masonary is described as brickwork concrete, plaster and similar but not thermally insulated. No code
 

Reply to 6mm cable 40amp breaker. 8.5kw shower in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
800
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top