Hi guys just want to run this one past a few of you genius dudes out there. Is the following ok...?

32amp mcb > 6mm cable > socket in loft > x2 2.5 (1 leg to underfloor heating in bathroom 13amp & 1 to summer element 13 amp both fixed) the socket has a shower pump permanently plugged into it with a 5 amp fuse. All RCD protected.

Now I know the 2.5 should have a 20 amp MCB normally but is this ok because they are run in parallel from that socket? Ie there isn't a section in the circuit that is just 2.5 with all the current going through. Thanks guys.
 
if each fixed item ( ufh and summer element) is on a 13A FCU, then it's OK.
 
Brilliant that's what I thought. Thanks for your prompt reply, was in the middle of a debate about it and now my pint this evening is all paid for. Thanks again.
 
There not in parallel as there not run to the same item of equipment there feeding seperate FCUs are they not?...

How far from the socket are the FCUs and how is it installed?. In certain circumstances over current protection can be omitted you need to look in the BGB.

Why dont you de rate down to 20A at the CU and then link them from socket to FCU to FCU?...
 
Brightspark, I understand what your saying. Is it possible to run from fcu to fcu? Would the first one not have more current than the manufacturer of the appliance intended?
 
Anyways to answer your question. Walls can be chased but we can't lift tiled floor and each appliance is on opposite wall to the other. So I need two run two cables one down each side.
 

Reply to 6mm down to 2.5? design question? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
355
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
908
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This contactor you suggested unfortunately only has two NO switches rather than 1 NC and 1 NO required for the CR3 current sensing bypass...
Replies
14
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top