I've been asked to change few double sockets, but not keen on touching after seeing 6mm cable, so did a bit of checking as can see the kitchen 'extension' has been wired in 6mm (red) with a 40amp MCB. The radial has 5 double sockets, including a dishwasher, tumble dryer, washing machine and cooker at end of circuit. She is about to sell the property and I'm concerned. She said it has been like this for over 20 years and never had a problem, would appreciate any opinion on this. Thanks.
 
in my opinion, it is not acceptable.
due to the fact the terminals on the sockets may become overloaded before the breaker trips.
20A max for a radial with 13A sockets in my opinion.
32A ring is ok as the load is distributed around 2 legs so its unlikely to have over 20A on any one leg.
 
in my opinion, it is not acceptable.
due to the fact the terminals on the sockets may become overloaded before the breaker trips.
20A max for a radial with 13A sockets in my opinion.
32A ring is ok as the load is distributed around 2 legs so its unlikely to have over 20A on any one leg.
I am also concerned about overload of cables and connectors, I was going to suggest to change the MCB to a 32amp from a 40amp.
 
What are the actual terminals rated at on a standard cheapo double socket ? Im sure I read somewhere they are rated at 20amps
 
The design guide in app 15 offers a 4mm2 radial on a 32A breaker for socket outlets, so presumably the terminals at the rear of socket outets can take 32A.

Whether 40A is acceptable, only the socket manufacturer can confirm. Maybe put the question to them? Be interesting to hear what they say. I did put this question to scolmore a while back, but I couldn't get them to understand what I was asking, and they stopped answering my emails after a couple of attempts.

You may also find that some socket terminals are not able to take 2 X 6mm2 conductors.
 
What are the actual terminals rated at on a standard cheapo double socket ? Im sure I read somewhere they are rated at 20amps
Since a double socket has a load potential of 26amps across the twin outlet, then I would assume that all socket terminal points are rated for 32amp since a 4mm2 32 amp radial is permissible also.
 
Is there enough room to make a 3 way joint in the back of the boxes?

Loop the 6mm through, and spur off the joint into the back of the socket.

Then the joint is taking the full load, not the socket terminals.
Just to also add there is a spur going to another socket on a 4mm cable. so behind 1 socket are 2 x 6mm and 1 x 4mm was thinking of using 3 wagos (221) 0.5-6 41A and blank that socket outlet.
 
With the eye watering price of copper cable these days I would be stripping all the 6mm cable out and re-wire it in 2,5

Keep the 6mm in the van for future cooker and hob hook ups
 
With the eye watering price of copper cable these days I would be stripping all the 6mm cable out and re-wire it in 2,5

Keep the 6mm in the van for future cooker and hob hook ups
LOL ...think customer would not be too pleased..In all serious do you think what I suggested is ok?
Blank plate on the socket containing the 2 x 6mm and 1 x 4mm put into 3 wagos (221) 0.5-6 41A, keep the 40A MCB in the CU.
 
I have used Wago to extend 6mm cable no problem

The issue is still you have sockets on a 40amp mcb and don't know the rating on the sockets
 

Reply to 6mm kitchen radial sockets with cooker on 40amp MCB in the The Welcome Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
951
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
Thats why somebody told you to spk to the sparky
2
Replies
18
Views
2K

Search Electricans Forums by Tags

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top