E.E.I
-
TNC-S system
60A BS1361 Fuse
16mm Tails
6mm Main Earth
6mm Bonding
Ze 0.30
PFC 0.9kA
So if the CSA meets the requirements of 543.1.3
s= sq route of I2t/k
Sq route ((900x900)x0.1)/115
I got the 0.1 from table 3A1 pg 319, looking at the graph it looks like its about 750A to blow in 0.1 but to stay safe say 800A.
s = 2.47mm.
does that sound ok?
would you say the 6 mm is adequate?