6mm or 10mm to an electric shower ? | on ElectriciansForums
Discuss 6mm or 10mm to an electric shower ? in the Australia area at ElectriciansForums.net
bristol
had a job last week ,the company i work for use a contractor now and again for jobs we dont have time to get to . the deal was they would run in a supply for an electric shower up to the isolator and when we are ready we would come in and remove bath , install shower cubicle and shower . after opening the isolator i found they had wired it in 6mm T&E , considering the run from the cu is about 8m and then from isolator to shower will be about another 7 m i decided to rewire in 10 mm because personally i feel that although 6mm can carry up to 38 amps showers should be wired in 10mm which can take up to 52A when run in trunking . just wanted to know if anyone else feels that wiring in 6mm is an easy option which should not be accpeted or is it acceptable just because its whithin the regs figures ?
There was a thread on similar the other day:
http://www.electriciansforums.net/e...rum/45042-8-5-kw-shower-6mm-tripping-mcb.html
Basically it will come down to the installation method for the cable IMO. Table 4D5 in the regs gives the current carrying capacities for twin and earth. Clipped Direct will give the best capacity as heat can dissipate more easily. As the table shows the capacities vary according to how the cable is installed. Taking it a step further there's all the de-rating factors to go in to. You then need to look at your voltage drop (Appendix 6 in the OSG).
Reply to 6mm or 10mm to an electric shower ? in the Australia area at ElectriciansForums.net
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
I went to look at a job like this a few years ago. My customer had a rental house, where there was an upstairs bedroom that had a newly built stud...
    • Informative