Hi guys,

I can not decide to fail this or not:

6mm t&e in domestic environment, cables in mini trunking, on a 40a MCB

I would use 10mm of course, but am seeing this in many flats so is it acceptable or its a fail on the EICR?

Tank you!
 
Taking it its a twin and earth cable ? No it can only carry 34A mate. MCB needs down-rating or cable up-grading to a 10mm to comply.

Page 276, BS 7671, reference method B
38A to be exact. but OP doesn't say what the load is. if a cooker, i would fot a 32A MCB. if shower, would have to check the KW.
 
true. 35A is close to the max. for 6mm in trunking. i'd be inclined to recommend a 32A (type B). that would never trip at 35A. designer has probably used ref. method C , giving him 46A for the 6mm. end of the day, it's your call.
 
"But the load current can change, somebody can replace the shower with a bigger one."

Anybody changing a shower over to a larger load must check if the mcb and cable and iso switch is appropriate before any works commence, therefore not your problem at the time of you doing your work.

If its pulling 35A at flc its a 8kw shower. 6mm cable, put it on a 32A mcb because it will never be run at full temp for an hour to trip the mcb.
 
my thoughts exactly . 32A MCB is the cheapest option, but, as malc. said, a code 2 will CYA. however, BS7671 does not allow a ref. method B for T/E ( enclosed in trunking), so designer has probably used ref. method C.
 
table 4D5 for flat sheathed cable

Yes it is but as you've already said flat t+e method B isn't listed? If you compare the values from both tables, flat t+e is the same throughout all ref methods (apart from clipped direct, t+e disperses heat better).

Because table 4D5 doesn't list method B I'll take it from table 4D2A as the closest comparison and I'd stand in a court room to defend it. The IEE must think that no one puts t+e in trunking lol.

Just thought I'd explain why I said what I said so it doesn't mislead anybody by looking at the wrong table.
 
Went to look at a fuse board change today the is a 8kw shower on a old 6mm t & e cable run is just under 10 mtrs its on a 30 bs3036 now. When i change the board i shall put it on a 32amp type b 60898 as the shower wont be ran at full load for long if ever ran at full load at all. The cable are surface in the airing cupboard and then under the floor above a plaster board ceiling with no thermal insulation. I shall make a note on the eic that if the shower is changed for a larger load then the cable will need to be up sized. If i came across a 6mm cable on a 40 amp breaker then i would be inclined to change it for a 32amp breaker. I would treat it the same as 1.0 or 1.5mm domestic up stairs lighting circuit on a 16 amp breaker.
 

Reply to 6mm t&e domestic on 40a MCB ?? in the Domestic Electrician Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thanks for your time and opinion.
Replies
11
Views
1K
In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K
  • Question
In the current book (18th, amendment 2) it is under regs 433.2 and 434.2 In most domestic situations the usual approach is the whole circuit is...
Replies
3
Views
532
  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
848

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks