greasemonkey

Currently has 6mm T&E feed from a 32A MCB
I need to replace the shower, but does my current setup need upgrading?
 
7.5kw at 230v == about 32 amps, and as the shower aint gona run all day, im gona go out on a lim and say its fine with what you have discribed. BUT!!! you will need RCD protection, no ifs no buts an RCD is a must...
 
replacing shower on it's own . test the existing cable. if it is all sound, then no need to upgrade. RCD protection should be fitted , even if only a like for like replacement.
 
i don't think there is a reg. in BS7671 re. RCD on a like for like replacement. however, the manufacturers instructions usually specify RCD, so that means you fit one.
 
yer but im sure even if there aint no reg, if just replacing the shower it would make you sleep better at night :) and im sure you will be taking responsibility for the install so it should really need to comply..
 
well. i would fit RCD, even if it meant fitting a stand alone unit next to CU ( assuming CU was rewireable 3036 fuses)
 

Reply to 7.5kw shower in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
161
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
997
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

Hi, i am wondering if anyone has any experience with a 7.5-8kw shower that has a pump or some sort of boost internally fitted? Working at a hotel...
Replies
0
Views
276
So I would say the most common example of a circuit requiring overload protection is going to be a radial or ring socket circuit. You are correct...
Replies
9
Views
841

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top