Customer wants underfloor heating in his bathroom and wants to use a B & Q Homelux mat. Downloaded manufacturers instructions and technical data to see if this mat complied with the above reg. As it didn't appear to be in compliance (fibreglass mesh as opposed to earthable metal) I emailed Homelux technical seeking clarification but this was ignored. Had a call to their technical helpline returned today to be told that the mat did not incorporate earthing but that the mat was designed for, and had been fully tested for, use in a bathroom and that thousands had been sold and were in use in bathrooms. Other makes of mat seem to be similar. Local wholesalers have not heard of a 'fine mesh metallic grid' for use in such circumstances which makes me think I may be misreading something
The builders proposed method of installation is existing concrete floor, insulation board, mat, waterproof tile adhesive, slate finish which, according to the manufacturers is exactly right. Surely there can't be thousands of EICs for notifiable jobs showing a departure from 7671 because manufacturers instructions have been followed?
The builders proposed method of installation is existing concrete floor, insulation board, mat, waterproof tile adhesive, slate finish which, according to the manufacturers is exactly right. Surely there can't be thousands of EICs for notifiable jobs showing a departure from 7671 because manufacturers instructions have been followed?