Given the last post has been closed I'd like to continue the thread, without the bun fight, if I may.

Tis true that the common element, pardon the pun, in basic electrical calculations is the resistance of the element.

But how do you assess that resistance accurately when most appliances are rated to run happily between 220V - 240V and the supply could have a supply voltage of anywhere between 216V - 254V ? with the added bonus that most appliances now are manufactured abroad and conform to the European EN standards of 220V

Coupled with that. You could measure the resistance of the heating element with an Ohmmeter, but that would be the cold resistance. We know from the temperature coefficient of resistance that resistance increases with temperature so the hot power rating will also change!

Given that there are too many variables to make an accurate assessment, we would have to take a probable average using the nominal voltage and the power rating given on the package.

With that in mind we have R = V^2/P = 230^2 / 8500 = 6.22 Ohms and a current flow of 37A

However, what if the actual supply voltage, such as we find in many TT installations, as an example is 245V?

We now have a current flow of 39.4A

Assuming this as a worst case the power of the appliance is now 9.7kW !

Given that the fusing factor for overload for a 32A breaker is quoted as 1.13, the maximum allowable current that would flow for a given period of time would be 36A. So we are now running hot. Not so bad if you can guarantee that the usage was limited to about 10 minutes or so.

The reason why I mention this is that I once went to see a job where the granddaughter had been using a newly installed shower of unknown rating from a 30A fuse carrier supplied by a cable unknown and had blown the fuse. When I questioned the woman about the installation it was obvious the new shower was installed by a person of unknown/dubious professional qualification with her blessing. I suggested that as a council tenant she should contact the council's clerk of works and at that point I left.
 
bloody good argument for a jaccuzzi bath instead of a shower. another point is that in a bath, your G&T doesn't get drowned, and neither does your reading material.
 
bloody good argument for a jaccuzzi bath instead of a shower. another point is that in a bath, your G&T doesn't get drowned, and neither does your reading material.

A bit like an automated bidet......

Word of caution.... Don't put bubble bath in your Jacuzzi and then leave it running
My ex partner had the shock of her life when she saw foaming bubbles appearing from under the bathroom door ! :)
 
do your calcs as you would normally then clamp meter ,bible , and power it up , clamp meter to check the current bible to help pray you got your calculations right
 
A heating load will be given as X KW at Y V. that is your base figure.

If you want to take it further look in to the properties of NiChrome wire. As it’s temperature increases so does it’s resistance. In the case of a water heater the heat dissipated maintains a steady state within the wire. It’s an interesting one to look in to. I’ll try to find the temperature coefficient table for NiCrome, I’ve got it somewhere.
 

Reply to 8.5kW resistive load. How do you know? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
369
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
933
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top