hi there
after some advice re the above problem when just doing a simple like for like shower replacement, as it keeps cropping up. 8.5kw showers, 6mm2 cable protected via a 32amp MCB. now i would usally protect a 8.5kw shower with a 40a mcb on a 6mm cable (ref mthod c) . now i know a 8.5kw shower ( 8500/240 = 35.4 A) will never really ever threaten to trip a 32Amcb. So what do you do replace the 32 with a 40 ? or just leave the 32 in place and note on the cert ?. My concern is that i dont know why it was fused at 32A in the first place, it could be re ref method or it could have been just installed wrong.
after some advice re the above problem when just doing a simple like for like shower replacement, as it keeps cropping up. 8.5kw showers, 6mm2 cable protected via a 32amp MCB. now i would usally protect a 8.5kw shower with a 40a mcb on a 6mm cable (ref mthod c) . now i know a 8.5kw shower ( 8500/240 = 35.4 A) will never really ever threaten to trip a 32Amcb. So what do you do replace the 32 with a 40 ? or just leave the 32 in place and note on the cert ?. My concern is that i dont know why it was fused at 32A in the first place, it could be re ref method or it could have been just installed wrong.