Hi guys,
want your opinion on a issue I have found while changing a consumer unit today.
I came across the shower wired in 6.0mm on a 32amp MCB (8.5KW). I know this will draw just over 35amps and could do with being upgraded to a 40amp MCB, but checking the install of the cable it is going through cavity full of insulation and then through the loft covered in insulation.
i know that the protective device will be overloaded but would you say that this would be a risk to leave on a 32amp MCB and would you be able to tell me how long it would take for the MCB to trip at 35amps as I don't have a regs book to hand to check the time current curve graph.
if you need any more info let us know.
thanks.