oldtimer

In my work we had our 5 year PIR and we were issued with the test results, There was 2 figures on the sheet one was the actual ELI and the other was the max ELI.

So I compared it and found that the max ELI figure was taken from the tables in the 17th edition book.

My question is that the onsite guide tables have the figures corrected to the "rule of thumb" figure of 80% so when I drew this to the attention of the testing company they said they complied with the 17th

Can someone clarify the correct use of the 80% rule of thumb figure.
 
Last edited by a moderator:
depends on test sheetyour usingand if it asks for max value or corrected value, if its max value then put it in from bs7671 but check it meets adjusted calc also
 
In my work we had our 5 year PIR and we were issued with the test results, There was 2 figures on the sheet one was the actual ELI and the other was the max ELI.

So I compared it and found that the max ELI figure was taken from the tables in the 17th edition book.

My question is that the onsite guide tables have the figures corrected to the "rule of thumb" figure of 80% so when I drew this to the attention of the testing company they said they complied with the 17th

Can someone clarify the correct use of the 80% rule of thumb figure.


The majority of test result sheets have a column for the max tabulated Zs figures from BS7671 and a second column for measured Zs

The 80% rule only applies to non temperature corrected tables such as BS7671, both the OSG and GN3 plus NICEIC tables are already corrected by 1.20 for conductor temp and 1.04 for ambient air temp thus the 80% rule does not apply

The reason the BS7671 max figures are used is so that correctuion can be made taking into account any differing conductor and air temperate at the time of testing which the 80% may or may not cover
 
Last edited by a moderator:

Reply to 80% rule in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
759
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
748

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top