I need to down rate 80A Fused Main Switch (KMF) fitted with 80amp HRC fuse to nearest rated fuse for16mm swa burried 2 core cable.
Believe this would be 63A. Can't seem to find one does anyone know best and fastest supplier or if there is one closer to the 78A max for the cable.
 
Do you know that the cable will take 63A? have you considered the voltage drop and installation method?
As for the fuse rating i've never heard of a 78A fuse. 63A is the nearest. Supply wise any good wholesaler should have one or be able to get one is a short space of time.
 
Thanks only looked online this evening so far.

25m of 16mm 2 core cable already burried direct in ground will carry 78A and supplying DB with max required demand of 63A. Voltage drop 4.41v and ok but existing 80A fuse in kmf switched fuse at orogin too high.



Thanks Des,
This fuse is only 60A with the max demand required of 63A. What is the next fuse rating to carry the full demand but not exceed the cable capacity? Thought ther was a 63A fuse?
 
Last edited:
Thanks only looked online this evening so far.

25m of 16mm 2 core cable already burried direct in ground will carry 78A and supplying DB with max required demand of 63A. Voltage drop 4.41v and ok but existing 80A fuse in kmf switched fuse at orogin too high.




Thanks Des,
This fuse is only 60A with the max demand required of 63A. What is the next fuse rating to carry the full demand but not exceed the cable capacity? Thought ther was a 63A fuse?

I wouldn't worry about it
If you look at the time/current charecteristics for a 1361 60 amp, even with full load of 63amp,it will take for ever and a day to blow
 

Reply to 80A Fused Main Switch (KMF) in the Australia area at ElectriciansForums.net

Similar Threads

D
  • Question
The revised arrangement - please check that I have fully understood the points made in the above threads. Obviously a qualified electrician will...
Replies
5
Views
3K
Deleted member 155212
D
  • Question
Gotcha, thanks for the info.
Replies
7
Views
2K
Just stick the 63amp fused connector before the Henley block , or Lucy block as you call it, and your all good, as for your 2nd point, , the...
Replies
1
Views
640
  • Question
Single Pole, Single Pole Switched Neutral, and Double Pole are all different things. Hager RCBO's are Single Pole. I was recommending Single Pole...
Replies
33
Views
5K
  • Locked
  • Question
@AnonDIYer you have had plenty of advise suggesting that what you intend to do is not practical and no one is going to give you a method for...
2
Replies
34
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks