9.5kw shower, 2.5mm cable..... | on ElectriciansForums

Discuss 9.5kw shower, 2.5mm cable..... in the Australia area at ElectriciansForums.net

R

Ross Trician

got a call earlier this week from someone asking me to look at there shower as they had had an electric shock from it. intially advised them to switch of at pull switch, (not able to do so in fuse box as it was ild wylex 4 way and not marked up, customer unsure how to pull fuses etc)

Ayway,told em if they hadnt sorted it I could get today. basically found 2.5mm cable in pull switch and in shower, checked rating, 9.5kw,,,,,that didnt add up...lol. unable to get any proper test results, readings all over the place, (tested to satisfy curiosity of termination in cu, wondered if it was say 10m in cu and choky block joint somewhere) told customer of cable faults etc, looked in loft and found a molten lump of cables and signs of heating on loft woodwork etc.

asked em who fitted shower, "it was the chap who tiled the bathroom about 3 years ago, he seemed to know what he was doing and it's
been ok for all this time"

Part P is a good idea but still wont stop these sort of peopl eh!!!!!!
 
the problem is..is this,too many jobs i go to look at,mostly people wanting upgrades,ie new sockets, you come across somthing like a shower in 2.5<that one rare thank funk>but you get my drift,customer says "iits worked fine for ages...."and thinks you having them on and not wanting to part with $$$ to put right, and yes to previous post, as long as long as they selling cable there be chancers to fit it............

i dont think they ever reach there full potential do they ?
ive had to modify my switch to go to 11 for the wife!!!:Ddunno whats wrong with her but the lights dim and i fear the disk in meter flying out the speed it turns!!!:eek:
 
Last edited by a moderator:
i was called to a shower problem once, the guy had wired a 7kw shower to his lighting circuit in 1.0mm, he told me he changed the 5a fuse to 30a after it had blown when he switched on shower.The only problem he had then was his 1.0mm lighting circuit cable had melted together from the consumer to the shower via all the bedroom pendants, I had to laugh at him as we was a neighbour of mine, so he then had to pay for a new shower cct in 6mm, and the rewire of his upstairs lights, this guy is supposedly not an idiot hes a trained mechanic, but it just goes to show how ignorant people are but they still have a go themselves, thats why part p will never work.
 

Reply to 9.5kw shower, 2.5mm cable..... in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top