I should know better but can’t get my head round this one and lost my notes from College.
On site guide is saying up to a 9.7Kw shower the cable CSA should be 16mm this seems rather high to me and impossible to work with.
I am fitting a 9.5Kw shower and looking at smaller CSA than 16 probe’s 10 but this will be for an assessment for a company and has to be correct can some one give me the formula for CSA, the fuse to be used are 40Amp and the total run is 11Meters from consumer unit to the shower.

Thanks Ian.
 
Not that your 9.7kW shower is likely to trip it but your shower is theoretically pulling 42A so having it on a 40A breaker doesn't look too good for an assessment. Haven't got any books with me but 6mm clipped direct has a surprisingly high CCC. :)
 
Thanks for your feedback any more please feel free Thanks Ian.
Electricians guide page 52 under : Upto 9.7Kw Shower and thanks i will find my paper work some where prob's in a cupboard
 
Hi and thanks for replying the run is up about 50mm on plastick trunking behind fitted kitchen unit and then to the loft space, this has from what i am told heavey duty lagging but will run over top and then down into a cupboard for switch D/Pole.

I was looking closer at the On site guide and found like a nut i was looking at all the wrong tables untill i got the correct one and i have used Clipped direct method. 2.5 has a 27Amp CCC i am calculating 10 mm should be ample for a 11M run

Thanks Ian.
 
I was looking closer at the On site guide and found like a nut i was looking at all the wrong tables untill i got the correct one and i have used Clipped direct method. 2.5 has a 27Amp CCC i am calculating 10 mm should be ample for a 11M run



I did say I thought you had the wrong table!!! Still wanted to see you terminate 16mm in to a pull cord... that would have been worth watching!!!

Are you "In" currently Ian.... I'll pop round as I'm headed "up the road"!!
 

Reply to 9.5Kw Shower on-site guisde? 16mm Twin & cpc? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
293
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
801
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
833

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top