Greg:
To make things worse the voltage is entering a shared Main Earthing Terminal from a separate premises with occupiers that don't seem to be that bothered about the situation. Things don't get better. In the section of the building which doesn't contribute to the voltage to the MET they've recently installed an electric shower. Its on a circuit with its own RCBO. Clearly the resi current part of the RCBO only supplies protection from earth currents generated within the equipment and not from currents supplied from external sources.
I got called to the building by the shower owning and guitar playing resident upstairs because of an apparent earth feedback problem on his electric guitar. So I checked the sockets and they all seemed to be be in order. And then, after checking there was no one downstairs and giving an instruction not to touch electric equipment or fixed items made of metal I started disconnecting earthing conductors.
After finding the 95 volts through testing I was intrigued to see the result when bringing the earthing conductor into contact with the Earthing Terminal. Sparks flew.
OK, a bit about the building. The ground (interesting term) floor is industrial. I guess the upstairs floor used to contain the offices related to the works. Supply goes straight upstairs and is now split to two meters (recently installed) and two visible DBs. There's also a large lever operated isolator connected to downstairs power. More on that later.
When the people downstairs returned they were good enough to let me take a quick look in the premises and after climbing my way over to a downstairs DB, which gave every appearance of being in operation and which the occupiers claimed was used to isolate non specified items of their equipment, I couldn't help but notice that the earthing conductor to this board had been cut and was hanging lose in the air.
A discussion with the people downstairs was called for. I received an explanation that all the problems were caused by the supplier and that they had tried many times to get independent supplies worked out for both floors of the building. I explained that this had nothing to do with the earth fault and that even though the Network Operator would supply a service head and meter there would be local responsibility to connect distribution and further explained that if for any reason there was a disconnection to earth and if someone was injured as a result then responsibility would lie with the downstairs property ... which, apparently, was not a problem. They are insured.
Any thoughts about this situation would be appreciated including in relation to switching off downstairs power when taking a shower. Not knowing what equipment they use downstairs I'm thinking that the people downstairs may need to be notified when power was about to go down and this complication is added to by the ~25 meter round trip that would need to be taken between the shower and the DB.
Edit: I forgot to say that the fault with the guitar turned out to be an unrelated problem with the pedal. It was only due to this mistake that I got the call out.
I got called to the building by the shower owning and guitar playing resident upstairs because of an apparent earth feedback problem on his electric guitar. So I checked the sockets and they all seemed to be be in order. And then, after checking there was no one downstairs and giving an instruction not to touch electric equipment or fixed items made of metal I started disconnecting earthing conductors.
After finding the 95 volts through testing I was intrigued to see the result when bringing the earthing conductor into contact with the Earthing Terminal. Sparks flew.
OK, a bit about the building. The ground (interesting term) floor is industrial. I guess the upstairs floor used to contain the offices related to the works. Supply goes straight upstairs and is now split to two meters (recently installed) and two visible DBs. There's also a large lever operated isolator connected to downstairs power. More on that later.
When the people downstairs returned they were good enough to let me take a quick look in the premises and after climbing my way over to a downstairs DB, which gave every appearance of being in operation and which the occupiers claimed was used to isolate non specified items of their equipment, I couldn't help but notice that the earthing conductor to this board had been cut and was hanging lose in the air.
A discussion with the people downstairs was called for. I received an explanation that all the problems were caused by the supplier and that they had tried many times to get independent supplies worked out for both floors of the building. I explained that this had nothing to do with the earth fault and that even though the Network Operator would supply a service head and meter there would be local responsibility to connect distribution and further explained that if for any reason there was a disconnection to earth and if someone was injured as a result then responsibility would lie with the downstairs property ... which, apparently, was not a problem. They are insured.
Any thoughts about this situation would be appreciated including in relation to switching off downstairs power when taking a shower. Not knowing what equipment they use downstairs I'm thinking that the people downstairs may need to be notified when power was about to go down and this complication is added to by the ~25 meter round trip that would need to be taken between the shower and the DB.
Edit: I forgot to say that the fault with the guitar turned out to be an unrelated problem with the pedal. It was only due to this mistake that I got the call out.