Its a 3 phase 99.9kw pv system, 3 x Tripower 17000TL inverters.
Distance from the inverters to the consumer unit is 160m!
Two options I can think of, the second im not too sure about...
First is to have a 4 core SWA cable (3 phases + neutral) buried underground all the way to the CU, but according to my software, to keep power loss uner 1%, it would have to be 95mm squared cable, and will cost over ÂŁ4,500!!!
I am trying to avoid this enormous cost, any suggestions?
The other thing ive thought about is to connect the AC to a nearer power outlet, not necessarily all the way to the CU... is that possible? advisable? any precaustions ?
Thanks
Distance from the inverters to the consumer unit is 160m!
Two options I can think of, the second im not too sure about...
First is to have a 4 core SWA cable (3 phases + neutral) buried underground all the way to the CU, but according to my software, to keep power loss uner 1%, it would have to be 95mm squared cable, and will cost over ÂŁ4,500!!!
I am trying to avoid this enormous cost, any suggestions?
The other thing ive thought about is to connect the AC to a nearer power outlet, not necessarily all the way to the CU... is that possible? advisable? any precaustions ?