Goody

-
Joined
Jan 21, 2010
Messages
638
Reaction score
94
Location
London
I am filling in an EIC for the electrical installation with a light & a socket circuit for the newly built “Out-house” (garage conversion) and I have used the existing link from the main DB.

At the main DB -> Ze = 0.10 Ω , PFC = 4.0 KA and R1+R2 of the 2.5 mm link cable from the main DB to the Out-house DB = 0.32 Ω

Should I now assume that Ze at the Out-house DB is 0.10+0.32 = 0.42 Ω?, if not, how do I calculate Zs for the Out-house lighting circuit whose R1+R2 = 0.42 Ω

Again on the EIC which “DB’s” details should I enter for “Main Switch or circuit-Breaker” and “DISTRIBUTION BOARD DETAILS” boxes? Please refer to the pictures. I think main DB's details are not relevant here.

Many thanks!

[ElectriciansForums.net] A bit of help needed here![ElectriciansForums.net] A bit of help needed here!
 
Hi Goody,

As you say the Ze or Zdb for your second DB is 0.42, your lighting circuit R1+R2 is also 0.42 (on this board ?) so I would say the Zs for this circuit is 0.84

Ze + (Rx1+Rx2) + (Ry1+Ry2) = Zs where x is the submain and y is the Final circuit of the second DB, if that makes sense
 
Last edited:

Reply to A bit of help needed here! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
275
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
773
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
779

Similar threads

Question 1 do you prefer buttered, salted or sweet salted? I'm guessing salty 😜 1. Auto range multimeter (used on mains before when testing the...
Replies
2
Views
606
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top