I quoted a job yesterday and thought it would be a good real life question on here to discuss and debate. Heres the info. (Marvo dont answer it please, let the trainees have a go first )
The building was a sports center but now the use of the building has changed to a place of worship. It has 2 changing rooms with shower cubicals, the customer wants 9.5Kw showers, 2 in the male changing room and 3 in the females changing room. The closest sub main board (C/U) is a cable run of 35 meters away and no spare ways available. Although that is not a problem, I will be picking up a supply from this point because the main incoming SWA feeding the board is big enough to handle the increased load of the showers and to feed the board (C/U) that consists mainly of lighting circuits and a couple of 16A socket radials.
My question is this:- How would you go about designing this project? Here are a few pointers to get you thinking....
5 x 9.5Kw showers at full load capacity = 41.3A each x 5 = 206.5A total.
Think about local isolation (35m away from the supply) How what would you design?
Size of cable rather for a sub main from the sub board or 5 x 10mm t+e? (installation method is:- on cable tray or in free air and does not need mechanical protection btw).
What is the volt drop on such a run?
A pull cord IP rated will be fitted near each shower fitting for on/off function and local isolation btw.
The rest of it is just putting a few water pipes together, I'm an electrician so that will be a walk in the park for people like us. Lets face it if a plumber can do it so can you lol. Done it loads of times as well by the way .
Over to you lot, post up what you think and how you would design this/these circuits. You wil all have to do things like this in time to come so get some practice in on here.
The building was a sports center but now the use of the building has changed to a place of worship. It has 2 changing rooms with shower cubicals, the customer wants 9.5Kw showers, 2 in the male changing room and 3 in the females changing room. The closest sub main board (C/U) is a cable run of 35 meters away and no spare ways available. Although that is not a problem, I will be picking up a supply from this point because the main incoming SWA feeding the board is big enough to handle the increased load of the showers and to feed the board (C/U) that consists mainly of lighting circuits and a couple of 16A socket radials.
My question is this:- How would you go about designing this project? Here are a few pointers to get you thinking....
5 x 9.5Kw showers at full load capacity = 41.3A each x 5 = 206.5A total.
Think about local isolation (35m away from the supply) How what would you design?
Size of cable rather for a sub main from the sub board or 5 x 10mm t+e? (installation method is:- on cable tray or in free air and does not need mechanical protection btw).
What is the volt drop on such a run?
A pull cord IP rated will be fitted near each shower fitting for on/off function and local isolation btw.
The rest of it is just putting a few water pipes together, I'm an electrician so that will be a walk in the park for people like us. Lets face it if a plumber can do it so can you lol. Done it loads of times as well by the way .
Over to you lot, post up what you think and how you would design this/these circuits. You wil all have to do things like this in time to come so get some practice in on here.