this is a real life fault i came up against. without over-complicating the issue of the site, i'll try to explain just the electrical side. OK. 10mm SWA 3 core feed to a wiska box. no RCD protection. from the wiska box there are 2 6mm 3 core SWA branches.lets call them 1 and 2. with minimal loads on both branches i got L-N 217V. L-E 238V. now applying a 2.5kW load to branch 1, 175V L-N, still got 238V L-E. however, no volt drop apparent on branch 2 at the load end. so then i'm beginning to doubt my original thoughts of a high resistance N conductor in the 10mm. further investigation found the faults ( yes, more than one fault which gave rise to the problem). right. lets have your thoughts on this. TRAINEES ONLY FOR STARTERS.
 
It is a really good head scratcher, Tel asked me earlier and this is a good fault to find. Have a go at it, throw your ideas up. Mentors PM Tel direct if you think you know?
 
with minimal loads on both branches i got L-N 217V. L-E 238V. now applying a 2.5kW load to branch 1, 175V L-N, still got 238V L-E. however, no volt drop apparent on branch 2 at the load end.

Do you mean (in the case where branch 1 is loaded) that (a) branch 2 L-N is 217V as before, or (b) branch 2 L-N is 238V ?
 
Steve trust you to have a go at this one. Interesting fault/s.

Tel is only talking about branch #1. Minimal load = 217V L-N, once a kettle is plugged in this drops to 175V???? L-E remains the same on branch #1.

This is Telectix thread, leave it to him to explain more when people have had their input and questions. I know the answer, he told me. Well he asked me and I just about worked it out, just. Tel likes to keep me on my toes lol :wink:
 
Do you mean (in the case where branch 1 is loaded) that (a) branch 2 L-N is 217V as before, or (b) branch 2 L-N is 238V ?

load applied to branch 1 caused the L-N at the junction of the 10mm and both 6mm cables to drop to 175V. however, no loss of power was apparent at the load end of branch 2.
 
well done to happysteve for getting it almost spot on. ( his answer was by pm, so the rest of you can still think about it without being influenced ).
 
Realise this is a few months out of date...
but my guess would be that there is a neutral to earth fault either on whatever is attached to branch one and or loose connection somewhere...?
 
the faults were basically.

1. high resistance in the N of the 10mm feed cable, causing massive volt drop in one branch.

2. the other branch had been incorrectly wired across L and E, so the volt drop L-N was not apparent.
 

Reply to a fault for trainees to get their heads round in the Electrical Course Trainees Only area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
810
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
857

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top