Darkwood
Check out the pics above; this was a callout to lost power in a factory, found 2 phases out blown 200amp fuses and a quick Meggar confirmed a short circuit between Y and B phases and unusual low readings to earth. id already isolated all outgoings and main switch was off to busbars but still dead short.
After totally stripping the dorman smith mccb board of incomming and outgoing mccb's only leaving the shell and empty busbars it yet again still showed dead S/C... at this point the only thing connecting between the bus-links was the paxolin insulation supports so as you can guess by now they had become conductive..... traced the reason to water leak settling on Paxolin and slowly cooking it till it charred up and result was a conductor shorting across the phases.
As a temp i filed down all the charring and raised the insulation value from a short to an acceptable 15Mohms but fitting back the mccb's reduced this as water must still be within the mccb's.... so until it rains heavy again they have business up and running and landlord has been made aware of what will happen if he dosn't get repairs done asap.
Im just a bit stunned that Paxolin has this trait that it becomes a conductor when charred, also yes its not a great concern anymore as it got banned years ago.
