hoppy

-
Joined
Mar 8, 2009
Messages
163
Reaction score
10
Location
Liverpool
Hi

I have a job supplying a garage cu. House is a TT system with 17th ed dual rcd board. From house CU to garage is about 35m. Ra is 28 ohms at house.
Customer wants small dual board in garage suppling 2 flourescent lights, alarm and a double socket for a compressor.

Unsure what to do for the best regarding the earthing. was thinking of running a 2 core 6mm swa to feed gargae cu and putting a rod in for the garage earth. But my question is, the house is a TT system and the garage supply cable will be on 32A MCB on and 30ma RCD protected at board, thus earthing the supply cable, but giving the garage its own earth (rod) and obviously rcd protection through an rcd main switch in the small cu. Will there be discrimination between the garage RCD and the house rcd as the earths are seperate, just cant get my head around this.

What would you do for the best???

thanks
 
sorry should have made myself a bit more clear. what i mean't is in theory i have two seperate earths TT rod at house and one at garage, the sheath of 2 core swa will be earthed at house end but not at garage end, so the earths are kept seperate.

Is this the best way to do it or should i connect the earthed sheath to the earth at the garage end, just thinking of any house faults going to earth through the garage rod.
Also if i keep the garage earthed seperately from the house, is there a nedd for an RCD at the garge if the supply cable is rcd protected.
All i am thinking is the only link from the house to the garage is the Line and neutral of the two core swa. so any earth faults in the garage will go via the garage rod so the rcd in the house will not trip, so i need an rcd at the garage cu.

Sorry if a bit confusing, been a long day and just can't get my head on this and don't know whta to do for the best.

Just looking to bounce some ideas off the more experienced guys on here

Thanks
 
I think your understanding of how a RCD works is a little confused!

The earth or seperate earth rods will make no difference as far as the RCD's are concerned they will only see a imbalance in the coil and trip.
Their would be no discrimination between the 2 RCD's and its anyones guess which one would trip first. (If both 30mA)

If you have the supply cable RCD protected with a 30 mA device then it would be pointless having a second RCD in the garage.

As far as the Rods are concerned link them all together and you will hopefully bring down the overall RA!
 

Reply to A liitle guidance please!!!!!!! in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
376
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
944
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
Many thanks all. Very helpful to be able to bounce these things around. Was fairly happy with it all initially, but once the seed of doubt is...
Replies
8
Views
840
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top