Hi
I have a job supplying a garage cu. House is a TT system with 17th ed dual rcd board. From house CU to garage is about 35m. Ra is 28 ohms at house.
Customer wants small dual board in garage suppling 2 flourescent lights, alarm and a double socket for a compressor.
Unsure what to do for the best regarding the earthing. was thinking of running a 2 core 6mm swa to feed gargae cu and putting a rod in for the garage earth. But my question is, the house is a TT system and the garage supply cable will be on 32A MCB on and 30ma RCD protected at board, thus earthing the supply cable, but giving the garage its own earth (rod) and obviously rcd protection through an rcd main switch in the small cu. Will there be discrimination between the garage RCD and the house rcd as the earths are seperate, just cant get my head around this.
What would you do for the best???
thanks
I have a job supplying a garage cu. House is a TT system with 17th ed dual rcd board. From house CU to garage is about 35m. Ra is 28 ohms at house.
Customer wants small dual board in garage suppling 2 flourescent lights, alarm and a double socket for a compressor.
Unsure what to do for the best regarding the earthing. was thinking of running a 2 core 6mm swa to feed gargae cu and putting a rod in for the garage earth. But my question is, the house is a TT system and the garage supply cable will be on 32A MCB on and 30ma RCD protected at board, thus earthing the supply cable, but giving the garage its own earth (rod) and obviously rcd protection through an rcd main switch in the small cu. Will there be discrimination between the garage RCD and the house rcd as the earths are seperate, just cant get my head around this.