Hi,

when calculating the min csa of main earth using the adiabatic what current value do you guys use?

Do you measure the PFC and use that, or do you calculate using 230V / Ze, or do you use the tables in BS7671?

Been reading up on it, and seems a bit of grey area on here!

Also would you go with a 0.1 sec or 5sec disconnection time for a BS 1361 man fuse?

Thanks
 
Thanks Tel

so say you measure the PFC as 3.1KA and its a 1361 100A, I take it you would use a disconnection time of 0.1 as 1450A is the largest fault current listed?

Thanks
 
Hi,

when calculating the min csa of main earth using the adiabatic what current value do you guys use?

Do you measure the PFC and use that, or do you calculate using 230V / Ze, or do you use the tables in BS7671?

Been reading up on it, and seems a bit of grey area on here!

Also would you go with a 0.1 sec or 5sec disconnection time for a BS 1361 man fuse?

Thanks
If you've measured the actual Pfc then use that.
Where this fault current value intersects with the time on the time/curve graph in the book use that time in the adiabatic equation.
 
Thanks Tel

so say you measure the PFC as 3.1KA and its a 1361 100A, I take it you would use a disconnection time of 0.1 as 1450A is the largest fault current listed?

Thanks

exactly that. don't forget that if it's a single earthing conductor ( not enclosed in a multicore cable ) the value for k is 143, not 115.
 
so for example,

PFC 3.1KA measured

3100 x 3100 x 0.1 = 961000

square root = 980.306

980.306 / 143 = 6.85

and for a TT with 100A 1361, with a PFC of say 30A

30 x 30 x 1 (1 sec disconnection time) = 900

square root = 30

30 / 143 = 0.209

Obviously the PFC on the 2nd calc will not take out the main fuse, just want tomake sure I have got my theory right with regards to the adiabatic!

Thanks


 
looks OK.but don't forget with a TT system, the PEFC might be considerably higher than you calculate from the Ze, due to parallel paths ( bonding).
 

Reply to A little bit of clarity! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
938
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
260

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top